Frankman60
Member
It’s good to know that APN works with the IOS app, because I am using the Tesla IOS app. So during the day I will know if the grid goes down. But when sleeping, I set my phone in Do-not-disturb (DND) mode and in that mode push notifications will not occur. That is something I wish Apple would change and allow “favorite” apps to push notifications through the DND mode. I think the only thing that can get through DND on IOS is a phone number (SMS text or phone call). That is done using an Emergency bypass setting in the Contact for a specific phone number, or including the specific phone number in the Favorites list. So when sleeping, I don’t think the Tesla APN would work for me.
Another method might an audible device that can detect the brief power interruption and beeps like a smoke detector. My home automation controller can detect a power outage and announce the outage, but I doubt it would detect the brief several hundred millisecond interruption.
Yes, I have the meter/main combo that you described. Thanks for the information.
Another method might an audible device that can detect the brief power interruption and beeps like a smoke detector. My home automation controller can detect a power outage and announce the outage, but I doubt it would detect the brief several hundred millisecond interruption.
Yes, I have the meter/main combo that you described. Thanks for the information.
People here have reported that the latest app does. At least on iOS, it generates APN (Apple Push Notifications). I'm still unclear on Android.
I take it you currently have a 200A combo meter/main with a 200A bus, and the plan is to have only one distribution breaker that panel, a 200A breaker to feed the new equipment? Then your contractor is correct, if you wanted to leave a 50A breaker in that panel for your 40A EVSE, then you'd have to use a 150A breaker to feed your new equipment to protect the bus. Or if you don't have solar, you could change the main breaker in that panel to a 175A breaker, then you can put as many breakers as you want in your main panel (without backup power), via the 120% rule: 175 + 30 * 2 < 120% * 200.
Otherwise, you would need a separate panel for the EVSE breaker, and this panel would be supplied via a feeder tap on the feeder from your meter/main to the Backup Gateway. That panel could be as small as a 2 space panel, like this one:
Murray 60 Amp 2-Space 4-Circuit Surface Mount Main Lug Load Center-LC002GSU - The Home Depot
Actually you'd probably want a physically somewhat bigger one, to provide space for the insulated mechanical connectors used for the tap. But you only need a 2 space, main lug panel with a single 50 amp 2 pole breaker: you can backfeed the breaker (meaning it needs a hold down) with the feeder tap, and then take your EVSE circuit off of the main lugs (using them as subfeed lugs).
It would still cost you a few hundred dollars to do that. You might be able to devise an alternative method to shut off you EVSE during a power outage for a comparable cost, with the added ability to manually enable EVSE charging off the Powerwalls if required.
Cheers, Wayne