Here's my chart. As you can see, the issue is that even during Peak, Solar is partially used to power the house (and not 100% sent to the grid). Again, all I would like is that during Peak, for 100% of solar to go back to the grid, and let PowerWalls power the house during that whole time.
I have mine set on TBC-Cost Savings mode.
Is there a way to reset or reboot the system, for it to start fresh?
My last true-up with Powerwalls had a net usage over 10,000 kWh. I really need to double my solar to cover my EV charging and future A/C install. No worry about poor excess compensation here.
I suspect there is something wrong with the power measurements you're seeing. Can you turn on the house load in the chart too so we can see what that shows? You should probably ask Tesla double-check your CT placement and configuration. The numbers in your chart don't add up. (Note that at 8pm, your Powerwalls were discharging 5.5kW and your grid was supplying the same, meaining your house would have to have been using 10.1 kW then. At 8pm, your Powerwalls go to standby and your grid draw doesn't change, meaning your house load would have had to coincidentally drop by the same 5.5 kW for the numbers to make sense.)
Edit: once Tesla fixes the CTs, I think your system should behave the way you want it.
Hi, sorry I'm a newbie and I don't know what "CT" refers to?
If the CTs are off/wrong, is that something I can fix/reboot/reset myself?
I've posted the 4 separate charts to break down that day. Hope that helps.
I don't think the CTs are wired wrong based on those graphs. You can compare to my post where they were wrong
There is more than one way for the CTs to be connected wrong. Here's what I'm seeing: house load just before 8 pm looks to be about 5 kW. The power being supplied from the Powerwalls at that time is about the same, as is the grid, so 10 kW total. That means there is an extra 5 kW coming from somewhere. I'm guessing the CTs that are configured as grid are actually measuring load or something like that.
I think it's pretty clear that there is a problem with the CT configuration. Tesla should be able to figure out exactly what is wrong.
I don’t think that’s the case. Just before 8PM the house load was about 5kW and the powerwalls were supplying the house 5kW at that time, but then it switched from peak to off peak. At that point the powerwalls stopped supplying power to the house and the house started drawing 5kW from the grid. They didn’t overlap and both provide 5kW at any point. That was just the point where it transitioned from one to the other. This is totally normal and expected behavior for the mode that he is in.
If it's not a CT issue, I am also baffled because I've been running cost savings for more than a year without ever seeing this behavior.
cwied: Just curious: when you first turn on your PW (or when you first started using TBC Cost Saving mode), did it immediately start doing what it's doing for you now? Or did it take a few days or weeks to learn your usage and eventually settled on your current behavior? (Am I correct to assume that your PowerWalls are discharging during your Peak, and allowing you to send 100% of your Solar to Grid at Peak?)
I've attached a chart of my system's behavior yesterday.
why does the Grid usage jump so much at 7pm?
I like that chart. What are you using to log and chart that data?
Looks like one of:I like that chart. What are you using to log and chart that data?
Yep, it's based on the first one. Here's the thread: New Powerwall Monitor
I'm running it in a Linux VM on my NAS server instead of on a Raspberry Pi, though.