That amps/speed chart assumes 240V. Many commercial installations are on 208V instead, since that's what you naturally get from three-phase commercial power. If this charger is on 208V, then knock off roughly 13% from those speeds. Possibly more if there's a lot of voltage drop, I've often seen under 200V at public chargers.
 
  • Like
Reactions: Mknac

AWDtsla

Active Member
Mar 3, 2013
4,289
4,266
NE
That amps/speed chart assumes 240V. Many commercial installations are on 208V instead, since that's what you naturally get from three-phase commercial power. If this charger is on 208V, then knock off roughly 13% from those speeds. Possibly more if there's a lot of voltage drop, I've often seen under 200V at public chargers.
13%? as you said it's often under 200V. Add 20% to charging times. It might be worse if the car reduces charging amps due to low voltage.
 

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.