No. Why do you say your panel support another 50 amps? Post a pic!If my panel cannot support an additional 50 amps for a 14-50 outlet can a switch be installed that would direct the current to the oven or Model X as needed?
If my panel cannot support an additional 50 amps for a 14-50 outlet can a switch be installed that would direct the current to the oven or Model X as needed?
Yes but a Dryer Buddy is an automatic switch which disconnect the EVSE (Electric Vehicle Supply Equipment) when the Dryer starts,That's conceptually. Looks like the Dryer Buddy is a much more elegant solution.
Yes, there are, but I really think you are jumping to an assumption you don't need to be, and there are much simpler alternatives.If my panel cannot support an additional 50 amps for a 14-50 outlet can a switch be installed that would direct the current to the oven or Model X as needed?
My house also has a 125A panel, and it was fine to add a 50A outlet because of this factor that does relate to your oven. Load calculations have a specific provision called "non-coincidental loads", which means loads that will generally be running at different times. So this is a perfect case of that. Your oven is a daytime load, and your car charging will be a nighttime load if you set it to start like at midnight or 1:00 AM or something. The load calculation then says that you can list these together but count the amps of only whichever is larger of the two. So if your oven is a 40A or 50A circuit, you could have a car circuit added at the same level, and it wouldn't change your load calculation at all.My panel, I think, is a 125 amp panel so looking at alternatives to changing the panel.
I love to have the "specifics" on that. I've never been able to find anything in the code that was less than pretty vague. 220-60 applies to non residential buildings. I've observed that 400 or 450 amps of breakers on a 200 Amp panel raise no eyebrows and have been assured by at least two separate electricians that that is the case. OTOH i have a 200 amp panels, installed by a licensed electrician, that has a 100 amp circuit for the Tesla, A 100 amp sub panel (with more than 100 amps worth of breakers on it) and probably another 400 amperes worth of other breakers in the main panel. Now I am confident that I have not overloaded the panels becuase many of these loads come on seldom if ever, heat and cooling don't come on simultaneously etc but more to the point I keep historical records and the most ever pulled out of that panel has been 170 A when an electric E-heater cam on while the Tesla was charging at 72 A. That condition persisted for 7 minutes and has happened only once since the 100 A Tesla circuit was installed. Thus I have, I think, a pretty good argument for an inspector should this setup ever be questioned but if there is something hard and fast in the code that I can use to see if I am compliant I'd like to check it out.Load calculations have a specific provision called "non-coincidental loads", which means loads that will generally be running at different times.
You are right, unless you bake pies for living, cooking occurs mostly around dining time. And dryer usage is similar.Load calculations have a specific provision called "non-coincidental loads",
which means loads that will generally be running at different times.
Well, it is 220.60, but I had not heard that the non-coincident load provision laid out there only applies to non-residential buildings.I love to have the "specifics" on that. I've never been able to find anything in the code that was less than pretty vague. 220-60 applies to non residential buildings.
That is another method that can be used in load calculations. Instead of all of the assumptions and approximations about 50% use for this or 80% use for that, you can substitute if you have logged usage data for at least 1 year. Then, you can demonstrate the amount of spare capacity you really have. I don't know the code reference for this one, but I've seen @eprosenx comment on it a few times, so he probably knows where that one is.I would only encourage OP to install the 14-50R if I had historical use data.
This is actually what most of the examples are for. It is considered a given that you are not running both the heating and the cooling at the same time, so those are frequently paired up in a non-coincidental load calculation.However heating and air cooling can occurs all around the day or night.
Well, it is 220.60, but I had not heard that the non-coincident load provision laid out there only applies to non-residential buildings.
NEC 220-60 Noncoincident Loads - Mike Holt's Forum
https://iaeimagazine.org/magazine/2012/07/16/article-220-continuation/
Satisfying Conditions
That is another method that can be used in load calculations. Instead of all of the assumptions and approximations about 50% use for this or 80% use for that, you can substitute if you have logged usage data for at least 1 year. Then, you can demonstrate the amount of spare capacity you really have. I don't know the code reference for this one, but I've seen @eprosenx comment on it a few times, so he probably knows where that one is.
This is actually what most of the examples are for. It is considered a given that you are not running both the heating and the cooling at the same time, so those are frequently paired up in a non-coincidental load calculation.
Since you have enough Amp capacity, in general it is simpler to use a tandem circuit breaker than adding a new panel.Had an electrician by today. He said my system can support the 14-50 but since I am out of slots I will need a new panel with open slots. The panel he is quoting me is $900 by itself.
Anyway, 220.87 is what allows you to use a year (or 30 days!) of data to justify adding load beyond the calcs.