MikeHolliday
Member
If you use 6 guage wire (THHN, THW, THWN, SE, USE, or XHHW as they are rated at 75 degrees and can carry 65 amps), 2 Conductors and a gound which is called 6/2. You do not count the ground as a conductor. On 240 volts for a Wall Connector you do not use a Neutral. You have Line 1 (Referred to as L1) @ 120 volts 60 amp breaker and Line 2 (Referred to as L2) @ 120 volts 60 amp breaker. If you use 6/2 it cannout be Romex. Romex is only rated at 60 degrees and only can carry 55 amps. Since the wire needs to be rated at or higher than 60 amps when connected to a 60 amp breaker.
As I mentioned above Tesla even points this out in the Gen3 Wall Connector manual on page 5. "If installing for maximum power, use minimum 6 AWG, 90° C-rated copper wire for conductors. NOTE: Upsize conductors if necessary."
Once again, Romex is only rated at 60 degrees and 55 amps (correction from earlier post) and therefore cannot be connected to a 60 amp breaker.
As I mentioned above Tesla even points this out in the Gen3 Wall Connector manual on page 5. "If installing for maximum power, use minimum 6 AWG, 90° C-rated copper wire for conductors. NOTE: Upsize conductors if necessary."
Once again, Romex is only rated at 60 degrees and 55 amps (correction from earlier post) and therefore cannot be connected to a 60 amp breaker.