Oh dang, I forgot to update on my
holes too....
So Sunrun came out to my house and they agreed the LB for the conduit housing the rooftop home run needs a drain hole on the LB.
But on the big U-shaped conduit, they came up with a novel way to interpret 2017 NEC 225.22.
@wwhitney will appreciate this.
So here's a pic of a "conduit" between my TEG2 and backup loads 200A load center. (PS, those are some damn sweet azz placards).
And here's the big U shape that goes from the TEG2 to the Enphase Envoy.
According to Sunrun's the NEC expert dude... he says there is no fundamental difference between the conduit in the first picture or the second picture. Since the first piece of conduit doesn't need any drain/weep holes, then the longer U-shaped conduit is also exempt from needing drain/weep holes.
I said "ok... but the short/stubby conduit is 'arranged to drain into both the Gateway and Load Center'... and both of those have weep holes in the bottom. So that means gravity at its lowest point will have drainage. However, the U shape has no drainage at its lowest point."
He countered saying this rule was meant to only encompass long-run conduits... and since the conduit between two sub panels is short there is no drainage requirement. That's why your outdoor AC condenser could have a conduit putting power to the compressor and there is no special drainage.
The guy took out his code book and it said for 225.22:
Raceways on exteriors of building or other structures shall be arranged to drain and shall be listed or approved for wet locations.
He said this language clearly exempts the U shape from needing drainage since the U is not a "raceway" it is just a short connector. He said Sunrun has installed conduit like this hundreds of times and never put in drainage for the U. He left after putting a hole in the LB next to the Envoy.
Edit: the expert also came to the conclusion I have too many disconnects on my house. He cannot fathom why I have 3 ways to disconnect energy coming from PG&E all sitting within 6 feet of one another. He said he has not seen Sunrun have to put a 200A big azzz disconnect on an install this tiny (7 kWp DC) in the Bay Area before. And he was like "wtf you have like 3 disconnects on each of the 3 batteries this is stupid." He counted that I have 9 more disconnecting means than what would be necessary to be code compliant. So at least he and I agree on something