I'm in Houston - so have a different utility, but would expect the results to be similar.
Before PTO, after the system is installed, the Tesla Gateway will be running, but the PowerWalls and solar panels will not be operating.
Our utility requires a large "generation disconnect" switch located near the electricity meter. Except for testing of the system, the disconnect switch is supposed to be in the "off" position, which disconnects the PowerWalls and the solar panels from the Tesla Gateway. This is to ensure the system has been reviewed by the utility before the PowerWalls and solar panels (which provide power) are connected to the grid.
Because the grid power goes through the Tesla Gateway to the house, there isn't any way to remove it from the grid to house circuit, so the Gateway will be running, but will likely be in the "system off" mode (since it has nothing to do until the solar panels and PowerWalls are connected.
While waiting for PTO, I did run some limited duration tests, putting the generation disconnect switch in the ON position so that I could verify the PowerWalls, solar panels, microinverters and Tesla Gateway were all operating as expected. Because if there was a problem, I wanted to get it fixed while we were waiting for PTO. But once those tests were finished, I disconnected the PowerWalls (each also has an on/off switch) and solar panels and put the Gateway back in "system off" model, because if the utility found we were using the system before PTO, that could make it difficult to get PTO.
During the limited testing, if there is sun and/or the PowerWalls have some energy stored, you can perform a quick "off grid" test by throwing the breaker in the Tesla Gateway panel. This will disconnect the grid power and verify the Gateway properly transitions to PowerWall/solar power - and that you don't have any problems with devices in your house. Once you've done that, you can reset the breaker in the Gateway panel and once the system transitions back to grid power (which could take 5-10 minutes), you can again do the generation disconnect and put the Gateway in off mode.
One thing you can't test until you have PTO is the powerline/solar cutoff frequency the Gateway uses when the PowerWalls are fully charged and you go off-grid while the solar panels are generating power. When you're off grid and the PowerWalls are full, there is no where for the solar energy to go - so the Gateway sets the powerline frequency high to shut down the solar inverter/microinverters. Tesla has been using 65Hz as the default frequency - which causes problems with some devices inside the house (UPS, refrigerators, air conditioners, pool pumps). If you experience any problems, request that your installer or Tesla lower the solar cutoff frequency (probably to 61 or 61.5Hz), whatever is needed to turn off your inverters/microinverters.