Just as a note, a 32A circuit breaker with a 32A load continually is not going to disconnect. Perhaps at 32.5A it MAY pop after a week of continual load. It's just so low in the thermal tripping curve.
Its okay to just say put it on a 40A breaker, but then you have to size cables for 40A rather than 32A.