If they each have their own 60 amp breaker AND the panel the breakers are in has the capacity to serve that load(and so on, back to the main panel!), there's no need to share the load.
Note that unless you are in an enormous house(with more than 200 amp service coming into the main panel), it is unlikely that main or subpanel will reliably serve two simultaneous 48 amp loads continuously along with the rest of typical house loads. You can't just hang a 125 amp subpanel off a main panel and start sucking 96 amps out of it continuously because the subpanel breaker/wiring is rated for 125 amps.
As far as one or two breakers, the answer is you need one(duplex) breaker for each of the Gen3 HPWCs. Whether those live in your main panel or a (presumably garage) subpanel is up to you and your electrician. If they are in a subpanel in the garage and you want them to both be 48 amp capable(60 amp breakers), you need the breaker in the MAIN panel and wire feeding the subpanel to be at least 120A(probably 125, since I don't think 120 amp breakers are made). Of course, you gotta add any other simultaneous garage loads to that calculation. If you had power-sharing configured, you would STILL want 60 amp breakers, but you could tell the HPWCs to not take more than a total of N amps simultaneously, and could therefore downsize the wiring and breaker going to the subpanel accordingly.
Note that unless you are in an enormous house(with more than 200 amp service coming into the main panel), it is unlikely that main or subpanel will reliably serve two simultaneous 48 amp loads continuously along with the rest of typical house loads. You can't just hang a 125 amp subpanel off a main panel and start sucking 96 amps out of it continuously because the subpanel breaker/wiring is rated for 125 amps.
As far as one or two breakers, the answer is you need one(duplex) breaker for each of the Gen3 HPWCs. Whether those live in your main panel or a (presumably garage) subpanel is up to you and your electrician. If they are in a subpanel in the garage and you want them to both be 48 amp capable(60 amp breakers), you need the breaker in the MAIN panel and wire feeding the subpanel to be at least 120A(probably 125, since I don't think 120 amp breakers are made). Of course, you gotta add any other simultaneous garage loads to that calculation. If you had power-sharing configured, you would STILL want 60 amp breakers, but you could tell the HPWCs to not take more than a total of N amps simultaneously, and could therefore downsize the wiring and breaker going to the subpanel accordingly.