My electrician installed 6 AWG with a 60 amp breaker for my Gen 3 wall connector. Said it was good for what I needed. Max amps it can pull is 48A anyway.60 breaker with Romex needs a 4 gauge wire. You can run a 4/2 and use a 6-50 outlet - neutral isn't needed. You also aren't allowed to put a 14-50 on a 60 amp breaker.
Romex (NM) doesn't go in a conduit. You can use 90C THHN for that. If you go that route, you can put a 60A breaker on 6 gauge. (Not an electrician, but I read a lot.)
My electrician installed 6 AWG with a 60 amp breaker for my Gen 3 wall connector. Said it was good for what I needed. Max amps it can pull is 48A anyway.
I have no idea what he used other than it's 6 gauge. Maybe because it's a 4ft run and the wire has more insulation? Just a guess. TBH I thought it would have to be 4 gauge too but in the end: they're the licensed electrician, I'm not, and if they say it's up to code and are willing to put their stamp of approval on it then I believe them.If he used NM (romex), that's against code. 55 amps is the max breaker 6 gauge NM for a 0.8 * 55 = 44 amp max continuous load.
According to this chart it's perfectly acceptable to run my 4 ft length with a 60A breaker and 6AWG copper wire. But again, I'm not an electrician, this was my electrician's call.So long as it doesn't burn your house down......
I'd turn it down to 40A just to be safe.
I ran #6 and a 50A breaker. Charged at 40A and the wire got plenty hot. So I turned it down to 30A. Plenty fast enough.
You're not reading the distinction. If the method used is separate individual wires in a conduit, then that has more free air space around it, and then yes, that can vent heat better and has a higher current rating, and 6 gauge wires CAN be used for a 60A circuit. But if it was Romex cable, where it's the wires bundled tightly together in that plastic sheath, they can't release the heat as well, so they have to use a lower temperature rating, and 6 gauge wires in that kind of cable CAN NOT be used for a 60A circuit.According to this chart it's perfectly acceptable to run my 4 ft length with a 60A breaker and 6AWG copper wire. But again, I'm not an electrician, this was my electrician's call.
Sounds good. Are you an electrician? Because I'm not and I really don't know what my electrician decided to do other than he put 6AWG on the work order so I know it works. Happy to ask him though.You're not reading the distinction. If the method used is separate individual wires in a conduit, then that has more free air space around it, and then yes, that can vent heat better and has a higher current rating, and 6 gauge wires CAN be used for a 60A circuit. But if it was Romex cable, where it's the wires bundled tightly together in that plastic sheath, they can't release the heat as well, so they have to use a lower temperature rating, and 6 gauge wires in that kind of cable CAN NOT be used for a 60A circuit.
My electrician installed 6 AWG with a 60 amp breaker for my Gen 3 wall connector. Said it was good for what I needed. Max amps it can pull is 48A anyway.
Paid $500 for a 4 ft run. Electric box is right outside my garage so they just drilled through the back, into the garage, and went a couple feet over. Took them about 2 hours to get everything installed. He's actually a friend of ours whose been doing this a long time so I didn't ask anyone else to be honest, not sure if he gave me a good rate or not (he claims he gave me the "friends and family rate") but considering this is the Bay Area, I figure it's not bad.Also being located in the Bay Area, do you mind sharing what you paid for installation?
No, it doesn't do anything with that neutral pin. That is actually a dummy piece of metal that is just there for structure, but isn't connected to anything inside the plug adapter.To start charging, does the UMC charger check if the Neutral wire is connected or not when using the 14-50 plug?
That would be exceedingly strange, as a 15-50 is a very odd and rare outlet type. I'm thinking this is a typo. Do you mean 5-15 or 14-50? Those are both pretty common.I am asking this question because I have two house. First has 6/3 wire and a 15-50 receptacle in the garage
No, definitely don't put a 14-50 receptacle, which is supposed to have all four wires, onto only a three wire line that is missing the neutral. Not only is that a code violation, but it can be pretty dangerous if someone were to ever plug an RV into that outlet with the missing neutral. I didn't know how this would work before until I saw some Youtube videos about it, but appliances or lights in the RV, which are expecting 120V, can get very uneven voltage levels across them, up to 240, and can blow up. It's not a good thing. So put the proper 6-50 on there and buy Tesla's 6-50 adapter.second has 6/2 wire to a disconnect junction box in the garage but no receptacle. For the second house, can I install the 14-50 receptacle without neutral connection or should I install a 6-50 receptacle and buy the Tesla 6-50 plug?
Well, that is a different specific code violation. Even though they are both nominally at 0V potential, NEC requires that neutral and ground lines be kept separate all through your house. There must only be one place where they are tied together, and that is in your main electrical panel. It's a violation to tie them in an outlet or in a subpanel.Rocky_H. Thanks for the answer. Yes, it is a typo, It is 14-50.
At first, I was thinking connecting neutral and ground together at the socket to prevent a floating neutral if someone else plug a 120V circuit (like a RV).
Well, that is a different specific code violation. Even though they are both nominally at 0V potential, NEC requires that neutral and ground lines be kept separate all through your house. There must only be one place where they are tied together, and that is in your main electrical panel. It's a violation to tie them in an outlet or in a subpanel.