    I have not seen the following all in one place:

    TESLA Wall Connector (2015 version and later) installation wiring suggestions (USA Only)

    Breaker SizeCopper THHN
    Wire Size
    (US NEC)
    Bare Copper
    Ground Size
    Conduit Size
    (US NEC)
    Amps
    to Car
    kW
    to Car
    Miles Per Hour (Single)Miles Per Hour
    (Dual)
    Full Charge
    Hours
    Single 85
    Full Charge
    Hours
    Dual 85
    2012121/2163.811112424
    3010101/2245.817171616
    408101/2327.723231212
    506103/4409.629291010
    606103/4N/A for Tesla Wall Connector
    70483/4N/A for Tesla Wall Connector
    80483/46415.42947106
    90381N/A for Tesla Wall Connector
    1003818019.22958105


    • For THHN wire. Which must be in conduit. If you use something else, EVERYTHING changes, and none of this applies.
    • This is for currently shipping (2014 and 2015) Tesla Wall Connectors only. If you are installing an older wall connector, an outlet, whatever... none of this applies.
    • kW calculated for 240V, which is commonly found in homes in USA. Commercial is usually 208V. Installs in a commercial building will have slightly different kW to the car.
    • All MPH and charge times are from Tesla publications (not calculated)
    • Extra long run (over 100 feet)... unusual temperatures... dragons regularly flame your garage... none of this applies.

    DO NOT BASE YOUR INSTALLATION ON THIS POST. Hire a qualified electrician, and/or read the Tesla install guides and all applicable codes yourself.



    Also, I was curious about the cost difference of 100A vs 50A service (assuming the supplying panel is capable) because I've ordered two chargers in my car and my neighbor ordered one. Yes, a neighborhood friend ordered an S85D just a week or so ago. So, here's an example calculation for my house, which will have approximately 70 feet of conduit/wire run between the panel and the wall charger. Costs are rough, and based on "big box" (Lowes/Home Depot) pricing, parts only:


    Example Cost in DFW area - Parts Only


    Breaker SizeHome Depot
    Cost Per Foot of wire
    Feet at Example HouseTotal for Wire OnlyEstimate for
    Conduit & Fittings
    Estimate for BreakersWiring TotalTesla Wall ConnectorTotal Total
    20$0.3970$81.90$30.00$10.00$121.90$750$872
    30$0.49
    $102.90$30.00$12.00$144.90
    $895
    40$0.59
    $123.90$30.00$14.00$167.90
    $918
    50$0.89
    $186.90$50.00$20.00$256.90
    $1,007
    60
    70
    80$1.19
    $249.90$50.00$30.00$329.90
    $1,080
    90
    100$1.39
    $291.90$75.00$40.00$406.90
    $1,157








    14.90%





    Cost increase for 50 to 100 amp, parts ONLY. ^^^^^
     
  2. Cottonwood

    Cottonwood Roadster#433, Model S#S37

    Joined:
    Feb 27, 2009
    Messages:
    5,062
    Location:
    Colorado
    I believe that with the correct insulation and other parts, it is possible to use #4 wire for a 90 Amp breaker and 72 Amp charging.

    The older HPWC's had settings for 60 Amp and 90 Amp breakers which were some nice cost sweet spots using #6 and #4 copper wire.
     
  3. tga

    tga Active Member

    Joined:
    Apr 8, 2014
    Messages:
    2,201
    Location:
    New Hampshire
    #3 tga, Jan 31, 2015
    Last edited: Jan 31, 2015
    Hopefully FlasherZ will give us a definitive answer, but I'll chime in.

    Ampacity of copper wire depends on temp rating of the insulation and terminators. See: Ampacity Charts or American wire gauge - Wikipedia, the free encyclopedia

    Note: Every amp rating below is a breaker rating for the circuit; charge current will be 20% lower.

    Your chart assumes the conservative 60°C ratings for 20-70A and 90A breakers. 4 AWG @ 80A and 3 AWG @ 100A requires moving up to 75°C wire and breakers (vs 70A max and 90A max, respectively @ 60°C)

    I haven't found anything that definitively states the temp rating of the terminals in the HPWC, but the installation manual recommends using 75°C 3 AWG wire on a 100A breaker for 80A charge current. This implies the terminals are 75°C rated. If you use 75°C wire and terminations, you can push 8 AWG to 50A, 6 AWG to 70A (rated for 65, round up to next std breaker = 70A), and 4 AWG to 90A (again, 85A, round up).

    Note that 2 AWG is the max for the the HPWC terminals, and people have pointed out it's hard to fit it in. Also, 3 AWG is a somewhat oddball size, and may need to be ordered.

    Personally, I would follow your recommendations and go by the 60°C wire ratings. The wire will run cooler, and you will get less voltage drop. When sizing wire, bigger is always better. As your second chart shows, the price difference is minimal. Note that this means using 3 AWG for 80A and 2 AWG for 100A.

    Edit: Of course I forgot - great post. It's nice to have conduit fill and ground conductor size in one place.
     
  4. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    I don't see anything that really sticks out to me, other than what's been pointed out already. There are lots of "it depends" scenarios that aren't covered - for example, temperature derating, etc. For the lower current ratings, NM cable requires 60 degC rating, while wire-in-conduit can use 75 degC; a NEMA 14-50 can be installed on #8 in conduit, but must be on #6 if NM (Romex).
     
  5. swegman

    swegman Member

    Joined:
    Mar 27, 2012
    Messages:
    962
    Based on my memory (which could be faulty), I seem to recall that 2AWG wire was less expensive than 3AWG wire. I also seem to recall that I paid about 0.85/foot for 2AWG wire from a supply house I found on the internet.

    I agree that 2AWG wire is difficult to work with (compared to the typical wiring found in a residential house).

    Also, as noted above, the older HPWCs provided for the hookups between 60A and 90A but not 20A to 40A. The current HPWCs dispense with settings for 60A to 90A hookups and added 20A to 40A hookups.
     
  6. Danal

    Danal electricmotorglider.com

    Joined:
    Dec 11, 2014
    Messages:
    431
    Location:
    Fairview, TX, United States
    #6 Danal, Jan 31, 2015
    Last edited: Jan 31, 2015
    Great feedback guys, thanks for all of it. Original post updated:

    1) Now specifies THHN wire. Which must be in conduit. If you use something else, EVERYTHING changes, and none of this applies.

    2) To be clear, this is for currently shipping (2015) Tesla Wall Connectors only. If you are installing an older connector, an outlet, whatever... none of this applies.

    2) Several other minor edits for clarity.
     
  7. Cottonwood

    Cottonwood Roadster#433, Model S#S37

    Joined:
    Feb 27, 2009
    Messages:
    5,062
    Location:
    Colorado
    A question about kW to car. It looks like this column uses a Voltage of 220 Volts. The vast majority of residential service is 240 Volts in the US, and much of the commercial, 3-phase service is 208 Volts. Why did you use 220 Volts; was that a compromise or average of residential and commercial?

    I have two HPWC's. One typically starts at 245 Volts at 0 current and sags to 240 Volts under load. The other typically starts at 247 Volts at 0 current and sags to 244 Volts under load. The latter one has a short 12' run of #2 copper from a 400 Amp panel.

    220/110 Volt, split-phase service dates to Edison's DC distribution system and is rarely seen today. Mains electricity - Wikipedia, the free encyclopedia
     
  8. Danal

    Danal electricmotorglider.com

    Joined:
    Dec 11, 2014
    Messages:
    431
    Location:
    Fairview, TX, United States
    Good catch. It should be 240 for a home, and 208 for commercial. That would also throw off all the times, etc... although I did not calculate those, I took them from Tesla's site. I wonder how they are making these calculations? We might be able to infer from "back" calculating. Anyway, I have adjusted to 240V, and pointed out in the disclaimers that 208 will be slightly different.

    Thanks!
     
  9. SteveS0353

    SteveS0353 Member

    Joined:
    Aug 23, 2014
    Messages:
    357
    Location:
    San Diego, CA
    I have one of those older HPWCs, and it has breaker settings from 40A to 100A in 10A increments (8 settings, with the 8th setting being the test mode). I have a 60A breaker, wired with #6 THHN, charge at 48A, and with dual chargers in the car, achieve ~35 miles of range per hour of charging -- enough to charge a depleted 85kWh battery after midnight.
     
  10. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    They have adjusted them over time, too. Originally, they used a 31 miles/hour charged on the 240V/40A column, and that was revised to 29 later.

    - - - Updated - - -

    Just as a quick clarification point - the conductor must always be sized for load - there is no rounding up. If the limit is 65A, you cannot present a load of 70A. You can use a 70A breaker to protect a 65A load and conductor against overcurrent, but the wire must be sized for the load.

    This means you cannot use the 70A HPWC setting on a #6 wire. #4 is required for 70A.

    - - - Updated - - -

    If this is the case, then you're fine with #8 for 50A (your chart lists #6).
     
  11. Danal

    Danal electricmotorglider.com

    Joined:
    Dec 11, 2014
    Messages:
    431
    Location:
    Fairview, TX, United States
    Yep, at 90 deg C. Unfortunately, my ability to update the post has expired.


    I could throw a technicality on the table and say it is THHN and at 75 deg C... then all would be correct... but that's cheating because THHN is rated to 90C... ;) So, instead, let me say:

    Excellent, excellent catch FlasherZ! Thank you very much.
     
  12. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    #8 is rated 50A even at 75 degC. You have to use the 75 deg columns with THHN anyway at the breaker because very few breakers, enclosures, and other termination equipment are rated at 90 degC anyway. And no problem - thanks for putting it together. You can report your own post and ask admins to update it.

    I usually tell people #6 anyway because of the tendency to use NM. Few people outside Chicago like the idea of doing anything more than EMT sleeves conduit-wise in homes.
     
  13. Danal

    Danal electricmotorglider.com

    Joined:
    Dec 11, 2014
    Messages:
    431
    Location:
    Fairview, TX, United States
    #13 Danal, Feb 1, 2015
    Last edited: Feb 1, 2015
    Would changing 50A to #8 (with a #10 ground) also then allow 1/2" conduit?

    If so, this could change my (single charger car on order) neighbor's mind about "going ahead with 100A for the future". He might still want to go big... but this change would bring the total 50A vs 100A cost difference to around 25%.
     
  14. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    If you're using 2 #8's and a ground, then yes - it's ok. If you're running a neutral, then no.
     
  15. tga

    tga Active Member

    Joined:
    Apr 8, 2014
    Messages:
    2,201
    Location:
    New Hampshire
    Thanks for catching that - round up breaker ratings, but not wire ratings.
     
  16. ged

    ged Member

    Joined:
    Jul 30, 2014
    Messages:
    22
    Location:
    Toronto, Canada
    What did people use for high amperage service disconnect or did you guys not have one?
     
  17. jcaspar

    jcaspar Member

    Joined:
    Aug 19, 2013
    Messages:
    793
    Location:
    Sacramento
    What about a column for those using NM wiring? I used 2/3 NM for my 100 amp sub panel and used 6/3 for my two 14-50 outlets.
     
  18. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    NM wiring requires you use the 60 degree column. 2/3 NM is good to 95 amps, and 6/3 is good to 55 amps. Technically, using 2/3 as a feeder to a small subpanel in the garage is improper if it is reasonable that you would use both 14-50's for EV charging at the same time, because the load calcs will require a 100 amp rated conductor. Some inspectors are likely to let it past because they're used to feeders being aggregate for a lot of small loads that can't possibly all run at the same time. For example, if you told the inspector that one 14-50 was for an RV and one 14-50 was for EV charging, you'd pass because it's highly unlikely that the RV's load would exceed the 45A you have left after deducting for the EV charging load.
     
  19. jeffro01

    jeffro01 Active Member

    Joined:
    Jan 30, 2013
    Messages:
    1,160
    Location:
    SF Bay Area
    This should be a sticky and updatable by the OP... :)

    Jeff
     
  20. Lloyd

    Lloyd Active Member

    Joined:
    Jan 12, 2011
    Messages:
    4,885
    Location:
    San Luis Obispo, CA
    In most jurisdictions in the US, it is acceptable to use the breaker as a disconnect if it is within sight of the EVSE. I put one in anyway. I recommend the Hubbell.