Desert Installation from April 2022. No problems since this past month but I rarely charge in the daytime as 99% charging happens before 7:30am departure. Electrical panel is on exterior and the Wall Connector is same wall but interior. 3ft distance max wiring maybe?
This month I have had to charge my car in the middle of day few times due to lots of air travel and the breaker will suddenly trip after about 45mins when set to normal 48amps. If I set to 45amps it seems I can charge for extended time.
I checked panel for anything major (char) and did not like the ground neutral installation I saw so I called another electrician out. Prior to that I called Tesla and they didnt see anything wrong with wall charger itself through charger diagnostics as it was charging on phone and even when the breaker tripped while on phone with Tesla.
New electrician said through visual only:
-Wiring is 6awg and should be 4awg. Reminder distance between panel and Wall Connector is minimal.
-Use metal conduit instead of the current plastic conduit inside the garage
-Neutral/ground install is bad. Has cut many main strands out to make it fit instead of using different bigger lug and the wire wraps behind busbars.
-Change the Eaton BR260 breaker with new (he didnt check underside to see if any issue)
-He did mention we can just change down to a 50A breaker and then I just commision charger to a lower charge rate for a 50A breaker.
Do you think the wiring size is the main reason why it trips during the day? I was initially thinking my panel is getting hot due to summer daytime heat, and that I am getting into a marginal derate condition for the breaker rating and therefore tripping right at or below the 80% of the 60A breaker.
Arent breakers calibrated/rated at 40C (104F) and therefore anything higher causes a lower trip point? It is 104F and more already in Vegas daytime not to mention other two 35A HVAC breakers heating up panel and then add in heat from 48 amp wall charger. I could see a 50C condition easily happening within panel.
Quoted me $300 parts and labor since he is close friend to my brother in law. So its not like its a major cost issue here plus would like to have it done to correct gauge. Just want to make sure we are tackling the real problem and not beefing up something we dont need to if the weak point is the breaker in the summer daytime heat.
Thoughts appreciated. Thinking to have him out this weekend to install.
This month I have had to charge my car in the middle of day few times due to lots of air travel and the breaker will suddenly trip after about 45mins when set to normal 48amps. If I set to 45amps it seems I can charge for extended time.
I checked panel for anything major (char) and did not like the ground neutral installation I saw so I called another electrician out. Prior to that I called Tesla and they didnt see anything wrong with wall charger itself through charger diagnostics as it was charging on phone and even when the breaker tripped while on phone with Tesla.
New electrician said through visual only:
-Wiring is 6awg and should be 4awg. Reminder distance between panel and Wall Connector is minimal.
-Use metal conduit instead of the current plastic conduit inside the garage
-Neutral/ground install is bad. Has cut many main strands out to make it fit instead of using different bigger lug and the wire wraps behind busbars.
-Change the Eaton BR260 breaker with new (he didnt check underside to see if any issue)
-He did mention we can just change down to a 50A breaker and then I just commision charger to a lower charge rate for a 50A breaker.
Do you think the wiring size is the main reason why it trips during the day? I was initially thinking my panel is getting hot due to summer daytime heat, and that I am getting into a marginal derate condition for the breaker rating and therefore tripping right at or below the 80% of the 60A breaker.
Arent breakers calibrated/rated at 40C (104F) and therefore anything higher causes a lower trip point? It is 104F and more already in Vegas daytime not to mention other two 35A HVAC breakers heating up panel and then add in heat from 48 amp wall charger. I could see a 50C condition easily happening within panel.
Quoted me $300 parts and labor since he is close friend to my brother in law. So its not like its a major cost issue here plus would like to have it done to correct gauge. Just want to make sure we are tackling the real problem and not beefing up something we dont need to if the weak point is the breaker in the summer daytime heat.
Thoughts appreciated. Thinking to have him out this weekend to install.