I use the standard 50 amp 240 adapter and have the charge current set to 12 amps.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
What Tesla adapter tip do you use on the mobile charger to connect to the quick220?
If someone has a Quick220 try replacing the outlet with a gfi and see if it can work or just trips out 100% of the time. I'm guessing as you start to draw real current (more than a couple amps) the separate return paths will differentiate by >.01 ma and game over.
House wiring convention is that all conductors must terminate in boxes open to room inspection. If you suspect cobjobbery then kill entire house and bring up breakers one at a time as you draw up a sketch.
--
I can verify it will trip before you even plug the car in even if only one leg is on a GFCI circuit. I've done it numerous times on road trips.
You can't pull any power at all out of a GFCI using a Quick220. A 120V GFCI is measuring current flowing on the hot and neutral. If there is a difference of a few mA, the GFCI trips.If someone has a Quick220 try replacing the outlet with a gfi and see if it can work or just trips out 100% of the time. I'm guessing as you start to draw real current (more than a couple amps) the separate return paths will differentiate by >.01 ma and game over.
Yes, but my point was it's difficult, if not impossible, to identify every junction on a particular circuit once the wallboard goes up and you can't see the romex/conduit. You would have to shut off the circuit in question, and open EVERY j-box in the house, check for voltage, and rule them out. That's the only way to definitively say that you have identified every junction in a circuit, and guaranteed that there are no 14Ga sections, and thereby safe to upgrade the breaker to 20A.House wiring convention is that all conductors must terminate in boxes open to room inspection. If you suspect cobjobbery then kill entire house and bring up breakers one at a time as you draw up a sketch.
--
ditto, but not without the road trips.
After use and research, I consider the Quick220 to be very problematic to use and unsafe in practice. Now, it's just a piece of charging history on my garage shelf.
With the Quick220, current is only flowing on the 2 circuit's hots, and nothing on either neutral. Both GFCI's will see that condition as a ground fault, and trip.
Yes, but my point was it's difficult, if not impossible, to identify every junction on a particular circuit once the wallboard goes up and you can't see the romex/conduit. You would have to shut off the circuit in question, and open EVERY j-box in the house, check for voltage, and rule them out. That's the only way to definitively say that you have identified every junction in a circuit, and guaranteed that there are no 14Ga sections, and thereby safe to upgrade the breaker to 20A.
I did this... I added the 240V indicator light across the two hots so I would know if they were different split phases. It has been discussed heavily that this may or may not be a good idea/legal/advisable but it is certainly possible. I limited the current to 12A to stay at 80% of the individual circuits’ rating. And two short extension cords (12g).
I use the standard 50 amp 240 adapter and have the charge current set to 12 amps.
Fwiw I used my home brew quick 220 last night in a rented condo (yes I build it with indicator LEDs and relays). The condo has a dedicated 20a circuit for the washer/dryer to plug into. It also had a dedicated 20a circuit for a hot water recirculation pump. Worked great.
My garage has 4 110V outlets. When I charge currently I get 120V/12A of charging.
Presumably each outlet is rated for 12A of current. Is there any way I could combine two outlets into one and get 20 amps of charging?
from the quotes I've received for Nema 14-50, the physical 50 amp wire and fishing through the basement into the garage is the largest expense.
I've been 'okay' with 12A but would be happier with 20.
It would be much less work and much more safe to just convert one of the dedicated 5-20 sockets to 6-20.
In a short term rented condo?
I have this rigged only for when I am traveling without better options available. I have a NEMA 14-50 in my home garage.You could also have a NEMA 6-20 outlet (240 V, 20 A) installed next to one of your 5-15 outlets. You'd need the Gen 2 Mobile Connector and a NEMA 6-20 adapter as well, which you can purchase from Tesla. I think this would be safer, and your car would automatically know the maximum current (16 A for a 6-20 connection).