I do not believe so as when you flip the switch on the inverter it goes into an islanding mode. The ONLY plug that is energized is the one below the switch. Below is from the owners manual and it tracks my testing.
5 Secure Power Operation
If the inverter has a secure power supply, you can use the energy from the PV plant directly via the connected socket-outlet in the event of a grid failure. The inverter automatically regulates the energy supply of the secure power socket-outlet according to the solar irradiation on the PV plant. While the secure power socket-outlet is in use, the inverter is disconnected from the grid and does therefore not feed into the power distribution grid. The secure power socket-outlet can not be used over-night,
because there is no solar irradiation available for the supply of the socket-outlet.
Requirements
☐ The inverter must be showing the error message 202, 203, 204, 205 or 801.
☐ There must be sufficient solar irradiation.
☐ Load with a maximum power of 1,500 W
Procedure for the secure power operation
1. Switch off the inverter miniature circuit-breaker.
2. Switch on the socket-outlet.
3. Plug in the load.
4. Switch on the load.
Do not connect any devices that require a stable electricity supply The power available during secure power operation depends on the solar irradiation on the
PV modules. Therefore, the power can fluctuate considerably depending on the weather or may not be available at all. In the event of solar irradiation being too low or overload of the socket-outlet, the voltage supply of the secure socket-outlet will also be interrupted. 20 seconds after interruption, re-establishment of the voltage supply will be attempted automatically. This can lead to the inadvertent starting of the connected loads.
• Do not operate any devices via the secure power socket-outlet that are dependent on a
stable electricity supply for their reliable operation.
• Ensure that the loads that are connected to the secure power socket-outlet do not require
more than 1,500 W.
Disconnection of the inverter due to insufficient irradiation
When the inverter disconnects itself due to insufficient irradiation, you have to switch back on the socket-outlet as soon as irradiation is sufficient.
Procedure once the power distribution grid becomes available again
If the power distribution grid becomes available again during secure power operation, the inverter
remains in secure power operation. The inverter only starts to feed in to the power distribution grid
again once the load has been disconnected and the miniature circuit-breaker is switched back on.
1. Disconnect the load.
2. Remove the plug for the load from the secure power socket-outlet.
3. Switch off the secure power socket-outlet so that the inverter begins feeding into the power
distribution grid again.
4. Switch the inverter miniature circuit-breaker back on.
Hopefully your installer added the switch and outlet as they did not come with the unit. They are located on mine directly below the touch screen. I was actually charging my Roadster in the shot below.