Dang ok....I don’t feel confident enough to do it myself....
Rich and or stupid. Contractors are always shocked when I know the basics. I had one guy that asked if I was a contractor because I knew that the exhaust pipe he was working on could use 2 45s instead of a single 90 pvc fitting.Try telling the electrician you need the NEMA 14-50 for an RV or camper, and not "tesla." Seeing how electricians dont publish rates and can just make up whatever they want, they probably subconsciously or consciously charge tesla owners more thinking we're rich.
i mean, we generally are well off but thats not the point haha.
I am guessing you know that when using conduit you will have to strip the outer jacket completely off of the 6/3 Romex you bought.I am doing it myself as we speak and I am in Southern CA. Bought all the parts this weekend. Fortunately, my location is 2' feet away from my main panel. Total cost.
50 AMP breaker: $9.48
4' 6/3 cable: $12.00 ($3 per ft)
4' 3/4" flex conduit: $4.00 ($1 per ft)
3 pack connectors conduit connector: $3.50
Wiring caps: $3.98.
Total: $32.96 + tax
Maybe add $10 for some weather sealant caulk and patching material.
If I was running 100', almost all your cost will be in wiring and conduit. Couple of junction boxes, materials should be about $450.
I am not an electrician but have some electrical/mechanical training and experience. Electrician can charge $60-$100 per hour and I think it'll be a 8 hr day's work for 100', at most. $1,000 is reasonable but $1500 is too much.
Everyone's situation is different. If you can break down what you're getting quoted on, that would help. Did you include the cost of a permit? The TWC? Any other oddities about your setup? It could be as little as $75 in my small town in Maine, where a permit cost me nothing, and I installed a NEMA Eaton 14-50 myself, with only 8ft of 6-3, conduit, 50amp double-pole Siemens breaker, or it could cost over $2000 for some installs, with long fat cable runs, and old panels that need rewiring, etc.I’m in Ma, called Tesla and they quoted me $1500 for under 100 feet from my breaker or $1800 for over. Is this reasonable? What have others done?
I went very simple: I had a never used 6-20 outlet (for air conditioning) that I relocated to the outside next to the driveway. No changes needed in the breaker box, although we replaced the old wire. Most of the work was poking the hole in the side of the house. Total cost $250. Of course, I'm limited to 16 amps or 15 mph for a M3, but I don't see a need for more.
I am guessing you know that when using conduit you will have to strip the outer jacket completely off of the 6/3 Romex you bought.
The can't run Romex in conduit is FALSE though commonly believed. Think about it some romex is burial rated but what do you have to do to protect it at ground level? Put it in conduit so the weed whacker doesn't get it. I think you might even run into inspection issues with stripped jacket if the inner wires aren't labelled.
That is something I learned here while researching my own HCWC install. I am not an electrician.This is a real surprise to me and when I read your post I immediately thought you were wrong as ALL of my time in construction (30 years) I have been told by ALL electricians and ALL city building inspectors that nm-b Romex is never allowed in a conduit as it will create to much heat build up, I learned something new today and can't wait to tell my current electrician that in fact not only does it meet code but is required to be in conduit where protection is needed (now if only I could convince a city building inspector, because even when wrong we know they are always right!) only place where you cannot use it in a conduit is in wet locations as the Romex is not rated for use in wet locations.
The can't run Romex in conduit is FALSE though commonly believed. Think about it some romex is burial rated but what do you have to do to protect it at ground level? Put it in conduit so the weed whacker doesn't get it. I think you might even run into inspection issues with stripped jacket if the inner wires aren't labelled.
From the 2014 NEC:
312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures. Conductors entering enclosures within the scope of this article shall be protected from abrasion and shall comply with 312.5(A) through (C).
(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure. Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
(a) Each cable is fastened within 300 mm (12 in.), measured along the sheath, of the outer end of the raceway
(b) The raceway extends directly above the enclosure and does not penetrate a structural ceiling.
(c) A fitting is provided on each end of the raceway to protect the cable(s) from abrasion and the fittings remain accessible after installation.
(d) The raceway is sealed or plugged at the outer end using approved means so as to prevent access to the enclosure through the raceway.
(e) The cable sheath is continuous through the raceway and extends into the enclosure beyond the fitting not less than 6 mm (1⁄4 in.).
(f) The raceway is fastened at its outer end and at other points in accordance with the applicable article.
(g) Where installed as conduit or tubing, the cable fill does not exceed the amount that would be permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto. Informational Note: See Table 1 in Chapter 9, including Note 9, for allowable cable fill in circular raceways. See 310.15(B)(3)(a) for required ampacity reductions for multiple cables installed in a common raceway.
I was looking for this code and could not find it, I was always told that the possibility of overheating was the reason, good to know that we can go up to 10' though, thanksRomex can be run through brief sections of conduit for protection and of course it needs to move through enclosures and fittings. It is NOT permitted to be run end to end through conduit of more than 10’ in length.
The primary concern of enclosing Romex in Conduit over longer distances is overheating and starting a fire.
I don’t know any electrical inspector who would pass an install in which Romex had been run through conduit over an extended distance.
Any Romex entering an enclosure for termination needs to have the sheath stripped back all the way to the housing so that the individual conductors are exposed.