In your case, your solar export is specifically controlled by your SE inverters, not by the gateway. If you don't have an SE RGM attached to your system then you can disregard the below information.
I'm assuming you have an SE RGM (revenue grade meter) attached to you SE inverters which allows you to change export limitation. You need to go into your lead SE inverter, via setapp and change the export control to 100 watts vice 0. This is to ensure your inverter will still produce when the power goes out during the day. If it's set to 0 export, in the event of a power outage, both of your inverters will shutdown and solely discharge from the PW's, no matter the SOC (state of charge) of your PW's. If you're willing to live with that, then you can set the export 0 and you will never export excess solar.
I have linked setapp pdf's below. Once you're logged in via setapp, you basically need to go to Power Control => Energy Manager => Limit Control => Control Mode => Export Control and set it to your desired export limitation.