- Test the voltage between the two hot legs. The value should be within 3% of 240v.
- Test the voltage between each hot leg and ground. The values should be within 3% of 120v.
- The maximum voltage drop should not be more than 5%. If it is, it violates the NEC, and it could be a clear cause for your problem.
I am going to challenge this line of thinking. Yes, the numbers are technically correct above, but applied incorrectly. The numbers above are *recommendations* in the NEC for voltage drop in feeders and branch circuits. (a feeder being the line from your main service to a subpanel and the branch circuit being from the last subpanel out to the end device) So a given feeder should not be more than a 3% drop and a given branch circuit not more than a 3% drop, but in aggregate it should not be more than a 5% drop (i.e. if you end up with a feeder with a 3% drop then you need to plan all branch circuits downstream of that subpanel with only 2% drop).
Now with that being said, the bigger influence here is likely to be the voltage your utility delivers. This can be within a pretty wide range. The utility itself is targeting 240v nominal, but this can range + or - 5% by itself (or even more for short durations!). Each utility may have its own standards, but PGE actually does quite a good job in documenting their targets:
https://www.pge.com/includes/docs/p...ergystatus/powerquality/voltage_tolerance.pdf
So your utility may say deliver power all the way down to 228v and be within spec. Your voltage losses within your house wiring are then *on top* of that (say down to 216.6 in that example).
Test procedure wise, measure your voltage two places before charging:
- At the main electrical service (typically your main panel)
- At the HPWC
Then start charging the car. Measure the voltage again at the HPWC and compare. This tells you how much total drop is happening when you place load on the circuit. But then measure at the main panel again as well. The delta between the previous and the new measurement tells you how much of the loss is "upstream" of your branch circuit.
FWIW, calculating loss on an electrical wire of a certain gauge and length for a given load is a VERY well understood thing. The NEC has formulas for it (and that is where the loss calculations to stay within 3/5% come into play)
Now with ALL of that being said.
THE NEC DOES NOT HAVE REQUIREMENTS ON VOLTAGE DROP
It has recommendations. Not requirements. Big difference. They don't see the issue as much as one of a danger. Instead it is more a functionality issue, a lot of devices won't work well or suffer reduced lifespans if voltages are too low.
If your voltage drop is over 3% or the feeder/branch wire is getting hot, it's very likely that the circuit was not installed with the proper wire gauge somewhere between the panel and the HPWC. This can cause a fire. Wire is rated for temperature ranges, and if yours is getting hot it can melt the insulation off, short out on the conduit or inside your walls, and someone could get hurt or die. Nobody should be messing with an electrical circuit that doesn't behave properly.
This is mostly correct, but it is also very possible and easy to have over 3% loss in a circuit just by having too long of a wire. While yes, this violates NEC recommendations, it is not a REQUIREMENT. While yes, if you have a lot of loss in a circuit that is not explained by the circuit length this likely indicates an overheated terminal or something (which is dangerous!), but if you just have a long circuit then the loss that causes the heating is spread out over the entire length of the wire and is factored into the load calculations for that wire. Wires warming during operation is how things work. The issue is about making sure they don't heat up TOO much (which is what reams of rules in the NEC are written to avoid).
So now on to my most important comment:
While inefficient, I don't think that voltage loss in really long circuits is any kind of a danger. In some electrical motors, if the voltage is low they will draw more amperage to compensate in order to keep spinning at their operating speed. But with a Tesla, it will always draw a precise amount of amperage from a circuit. If the voltage drops then it just charges the car slower (same # of amps, but at lower voltage the total amount of energy it can consume is reduced). I have heard of folks with over a couple hundred feet of wire in order to get to their parking garage from their condo. While not optimal, it should be fine.
The practical issue is that the Tesla vehicles are comparing voltage from when they started charging to the current voltage as they charge. Since the vehicle has no idea *why* voltage is dropping, it assumes any drop over a certain amount is due to a dangerous situation and it will backoff the charge rate or stop charging to reduce the risk. So if you drag the voltage down too much due to a really long wire you may run into this issue.
It is also worth noting that at certain times of day it may be just fine (right on the edge of what the Tesla will accept), but then maybe changing grid conditions during peak time of day cause it to trip.
So following the NEC guidelines is generally a really good idea, I could see cases in which you might be willing to go outside their specs for the specific special use case of EV charging.
Larger gauge wire gets more expensive in a hurry! (not to mention larger conduit costs and labor costs to run it) Have you looked at the price of copper lately?
I am curious if there is a true financial case to be made around wire upsizing due to the ongoing operational costs of energy loss. Where I live, power is pretty cost effective so the payback period may be a really long time in many situations.