I just heard from the electrician. I had emailed, with photos, late last night.
One of the guys who did the installation is on the way here, and will be bringing 100 amp fuses, "in case he can use them." When I asked about that, and why 80 amp fuses were installed in the first place, the answer I received was that the guy thought he remembered that the wire from the charger was only rated for 80 amps.
Now of course that makes no sense to me, if the charger needs a 100 amp circuit to charge at 80 amps. I'm about to go see what I can dig up in the HPWC manual, but if someone sees this in the next few minutes and could respond with, "The cable from the HPWC is x and is rated for y" that would be helpful, as I could then repeat that when the electrician shows up.
Thanks!
Edit: I found this in the manual--
--
NOTE: For most branch circuits of 100A, use 3 AWG (26.7 mm2), 75°C(167°F) copper wire. For installations less than 100A, use conductors thatare sized according to local electrical codes.
--
So it appears what wire to use to connect to the HPWC was up to the electrician.
Also I believe I recall reading that it was possible to connect #2 copper, but that it was tight, and took some skill. In fact I think the electrician who installed my other HPWC (about 60 miles away) commented on it. Looking at the pictures of this installation can someone tell me if these guys did connect #2 copper to the HPWC or not? (They were supposed to.)
Thanks!
Edit 2--
I think I answered my own question. See picture below. It appears to me that the cable running to the disconnect is quite a bit thicker than the cable running from the disconnect to the HPWC. I'm guessing they used #2 copper as stated to the disconnect, but then decided to use smaller cable to the HPWC. Is this something I should complain about, and ask them to rewire?
Edit 3:
This is what FlasherZ had to say about #2 copper and making the connection to the HPWC--
You can fit #2 into the terminals carefully, but it's tight - you have to make sure you get all the strands in there. I believe Tesla's installation specifies CU-only. If you use AL, they recommend taking it to a disconnect or junction box just before the HPWC and using proper connectors with the final length of copper.
I'm wondering if this means that the smaller gauge wire from the disconnect to the HPWC is really no big deal, assuming it is at least #3 copper.
Still wondering if I should push for the #2 copper that I asked for, and that the other electrician did install.