Thanks Henry. Even though I'm pretty careful and knoweledgable about electricity, it really sounds like the effort isn't really worth the return it would provide.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
I would so love to see a Tesla adapter to allow me to plug into two NEMA 14-50 outlets and charge at 80 amps with my dual chargers! I'll even buy an extension cord to reach into two RV park outlets. Would something like that be possible?
That will never happen!! Not in your lifetime...
Extension cords and supplying two sources of power to a single device (EV, EVSE etc.) is not allowed by the NEC.
Also the receptacle polarity is not specified, guaranteed or defined so they could be opposite on each receptacle producing a short between phases. KaBOOM!!
Also, just because there are two receptacles doesn't mean you can draw anywhere near a balanced current from them.
That is, based on the voltage drop in each branch circuit wiring you may only be able to draw full current through 1 of the 2 receptacles if the circuits are summed together at the charge port!!
Electrical code question:
Can I run two parallel NM-B 6/2 from my 100A breaker to the HPWC? That would give a sum of 110A allowable ampacity.
Reason for this question is that the highest NM-B (on 2 awg) ampacity I've seen is 95A,
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet6
which would be illegal on a 100A breaker and I was hoping not to run conduit inside my wall.
Electrical code question:
Can I run two parallel NM-B 6/2 from my 100A breaker to the HPWC? That would give a sum of 110A allowable ampacity.
Reason for this question is that the highest NM-B (on 2 awg) ampacity I've seen is 95A,
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet6
which would be illegal on a 100A breaker and I was hoping not to run conduit inside my wall.
...The NEC requires that a disconnect be located within sight of the load. I am not sure if the wall charger has a built-in disconnect (it has to be a mechanical means of disconnect) so I put in a 100 Amp non-fusible disconnect that is a 3 pole disconnect since the wall charger requires a neutral and 2 power (hot) conductors. ...
Electrical code question:
Can I run two parallel NM-B 6/2 from my 100A breaker to the HPWC? That would give a sum of 110A allowable ampacity.
Reason for this question is that the highest NM-B (on 2 awg) ampacity I've seen is 95A,
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet6
which would be illegal on a 100A breaker and I was hoping not to run conduit inside my wall.
splices are not allowed in the load center.
IMHO, Few electrical devices are used to their full potential and/or capacity and that is a good thing!!
With that, the HPWC (designed for 80 amps) is the most reliable and most safe way to charge the MS even when you are limited by the single charger in your car; at 40 amps or below.
That is, a hardwired device such as the HPWC which is UL Listed will most often be more reliable and less hazardous than any device connected by a plug/receptacle and given a Tesla will be most often charged: unattended - at your home - overnight, I will always opt for the robustness and a safety margin to reduce the possible hazards associated with frequent use.
So while the UMC may be a good device the plug adapters and residential receptacle will be the weak link.
Also, at 40 amps, the maximum current for the NEMA 14-50 plug/receptacle and the UMC, a non-NRTL (Nationally Recognized Testing Lab) device, are used to their design limit.
Therefore, I am saving my UMC for the occasional on the road charge and use the HPWC for the daily charge duties at my home.
For me the HPWC and installation cost is inexpensive when I consider piece of mind.
No. Set DIP switches in the HPWC to match the circuit breaker, not the car. The HPWC advertises it's maximum, and the car draws the lesser of the HPWC's max amps and the car's max amps. That's why public L2 stations (whether Tesla or J1772) can be used freely with any car that can plug in. A Model S with a single charger will limit itself to 40a.... Question: If I have a Model S w/o dual charger and use this Wall Charger, do I have to set some dip to 40A per discussion in this thread (Wall Connector Installed Today) and change the DIP SWITCH again if I ever get a dual charger on the Model S?
Electrical code question:
Can I run two parallel NM-B 6/2 from my 100A breaker to the HPWC? That would give a sum of 110A allowable ampacity.
Reason for this question is that the highest NM-B (on 2 awg) ampacity I've seen is 95A,
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet6
which would be illegal on a 100A breaker and I was hoping not to run conduit inside my wall.
The HPWC 100 amp circuit has an ampacity of 80 amps (100amp * .8 = 80 amp continuous) so the #2 AWG wire is good.
Parallel wires in the NEC is a rare exception and a branch circuit is not one of them. Also, only one wire can be used in a breaker terminal and splices are not allowed in the load center.
The NEC does allow you to use a lower rated wire/cable than the circuit breaker rating protecting the circuit. But there are exceptions for this and I do not recommend doing this.
Residential installs don't require conduit.
I've been wondering about this same question. Tesla gets away with it in their cables which makes them feel smaller and more flexible.
The NEC requires that a disconnect be located within sight of the load. I am not sure if the wall charger has a built-in disconnect (it has to be a mechanical means of disconnect)
I don't believe this last statement is true (agree with all your other points). Can you tell me what section of the NEC prohibits splices inside the load center?
No. Set DIP switches in the HPWC to match the circuit breaker, not the car. The HPWC advertises it's maximum, and the car draws the lesser of the HPWC's max amps and the car's max amps. That's why public L2 stations (whether Tesla or J1772) can be used freely with any car that can plug in. A Model S with a single charger will limit itself to 40a.
The answer is no. NEC 310.10(H). Only conductors of gauge 1/0 and higher may be paralleled except in special circumstances.
- - - Updated - - -
#2 is only good if it's wire-in-conduit and not NM cable. #2 NM cable is good to only 95A, and therefore does not work for an HPWC set at 80A. NEC 310.19 and 334.
- - - Updated - - -
However, the wire/cable MUST be rated for the full load. If you have an appliance that requires a circuit rating of 100A, you may NOT use a 95A-rated cable and the accompanying OCPD "upgrade" (240.4) to go to 100A. You size the cable to the appropriate load, then protect it with the proper breaker (which can be the next trade size larger, if the load is not a standard trade size).
There are exceptions to this - Chicagoland requires conduit and some select New Jersey & New York cities still require conduit for all electrical infrastructure.
- - - Updated - - -
Appliances don't follow NEC, which is for infrastructure wiring. The HPWC uses a #6 wire for 100A requirement, which would be illegal in an infrastructure install.
- - - Updated - - -
For what it's worth, one AHJ near me allowed the circuit breaker in the basement to act as the article 625 disconnect as long as the entire panel was lockable. Yet others have demanded one near the HPWC. This is one where you're going to get many different interpretations.
- - - Updated - - -
Splices are indeed permitted inside load centers. Many times, this is how generator panels are added after the fact - the existing circuit wires are spliced and carried into the transfer switch panel. They may not be pretty, but they're permitted.
thanks FlasherZ! You sound like one who really knows what he is talking about.
Thinnest legal means of connection that I can find then is two #3 THHN with #8ground in a 1" conduit (just under 40% fill). Minimum 5" bending radius! Anybody disagree?
For 80A charging / 100A breaker, this is correct (assuming copper). 5" bending radius on continuous raceways (there are some other options you have with surface-mounted rigid conduit and pull elbows, but the cover must be accessible, and it wouldn't be very thin). Thinnest is going to be EMT on the raceway IMO.
I would be very surprised if anyone would be able to run the proper size Aluminum into the terminals. They are very tight. I highly recommend just running the appropriate gauge copper. The cost savings are not worth risking a fire.
I got the Tesla wall charger today. I would like to mount the charger in the midpoint of where the MS will be located in the garage (still waiting on the MS to be delivered). This is not the location that Tesla recommends. I am concerned about having the charger near the garage door and having rain, snow, etc. on the charger and cable while charging the MS. I understand the wall charger has a NEMA 3R rating (this means it is somewhat weatherproof). Anyone have comments on locating the charger near the middle of the MS?
Thanks.
I would be very surprised if anyone would be able to run the proper size Aluminum into the terminals. They are very tight. I highly recommend just running the appropriate gauge copper.
I totally agree. The #4 I ran barely fit in the HPWC. I can't even imagine trying to get #3 in there for the 80 amp circuit/100 amp service.