Per the submitted drawings, the main service disconnect is supposed to be 1600A.
Based on these calculations that is only 1300kVA.
Maybe some overhead for expansion? It looks like there is room for a 4th cabinet. They were supposed to be place 3 in a row but that is not how they actually placed them.
Based on these calculations that is only 1300kVA.