MJ_CA_2019
Member
That is interesting.. I'm on PG&E NEM2MT and my interconnection agreement says:If you log into the web portal of the Tesla gateway and click summary it's the last line. I don't know if it's in the app anywhere. I have 2xPW and my site export limit is set to 8kW. So if I have export all enabled and it's peak pricing the gateway will send all solar to the grid and make up the rest up to 8kW, while still providing for the home load as well. As the sun gets lower the amount of draw from he PWs goes up. I don't know where/who set the limit originally and it does not appear to be user configurable.
2.7.3 Total maximum level of power that may be exported by the Generating Facility: 26.025 kW
However, the "site limit export" from the summary says 10.77 kW (I have 3 PW2).