I recently got a PW installed by a certified Tesla installer (not Tesla themselves)(see end of post for setup). It was the installer's first job and I had to self diagnose quite a bit. There were multiple CTs that I had to flip myself via the TeslaPros app and I had to double the solar CT (which is a common thing).
When I charge the Tesla at night (solar is not producing), and I do some tests charging the Tesla off the battery and off the grid (controlled by the backup percentage. If I set it to higher than what the Powerwall has right now, it will start charging from the grid and vice versa). But the Tesla app shows the draw from the grid always as much lower than the draw from the battery, despite no other changes of load around the house.
Here is a nice chart that shows this well. I got al the data via API calls to the Gateway and the Tesla Wall Connector (the red line). The green line and the white line should both be around the height of the red line.
What could be reasons for a misconfiguration either in software or hardware?
Setup:
When I charge the Tesla at night (solar is not producing), and I do some tests charging the Tesla off the battery and off the grid (controlled by the backup percentage. If I set it to higher than what the Powerwall has right now, it will start charging from the grid and vice versa). But the Tesla app shows the draw from the grid always as much lower than the draw from the battery, despite no other changes of load around the house.
Here is a nice chart that shows this well. I got al the data via API calls to the Gateway and the Tesla Wall Connector (the red line). The green line and the white line should both be around the height of the red line.
What could be reasons for a misconfiguration either in software or hardware?
Setup:
- Non-Tesla solar with Enphase inverter
- 2 PWs with partial home backup via backup panel (two breakers got pulled into that one)
- the two primary CTs are built into the Gateway
- the solar CT was clipped onto the right cable by the installer and matches the Enphase data (after doubling it)
- the main panel is upstream of the backup panel
- Two additional CTs were clipped around the two steel lugs in the main panel and correspond to the secondary CT2 & CT3