I have not once intended to suggest installing a 5-15 outlet into your house with 240V.
the only concerns you have using a 5-15 connector with 240V are the following:
... there is no reason to buy another adapter if you're being mindful of your wiring.
- Can the mobile connector accept two hot wires (120V in dual phases) on a 5-15 connector (i.e. is it wired to accept this internally)
- Amperage pulled through the line does not exceed original specs of 5-15 connector (i.e. 15 amps)
... if there happens to be 240V at the hot and neutral, it should just work as if you had a Tesla 6-15 connector on it. The real risk is you might accidentally plug in a 120V only plug into your now 240V outlet without thinking. THAT is the real danger. There is no electrical or physical reason that this setup is dangerous; it's just the idiot factor you have to worry about.
If you're being careful, physically, there is no danger to using a 5-15 for 240V. Just be sure of what you're plugging in.
Actually, in each case, my intention was discussing the 5-15 on an extension cord. I can see now why that is not how it was interpreted though. I wish I could edit those to add that, but I can't, sadly.That is indeed exactly what you suggested, twice:
Actually, in each case, my intention was discussing the 5-15 on an extension cord.
Actually yeah, that's what I'm describing, somewhat, although I don't understand why it's quite as you describe.How would you even do that? You're not seriously contemplating creating a Y-shaped extension cord with two 5-15P plugs that are then wired such that their respective hots go to each side of a 5-15R receptacle are you?
This is called a "suicide cord" for a very good reason. If the outlets you happen to plug it into aren't on separate circuits it will immediately create a phase-to-phase short. That is virtually guaranteed to damage equipment or start a fire.
And in any case, there is already a company (who actually knows what they're doing) who has created a safe way to do this: 110-120 and 220-240 Voltage Converters & Accessories
How would you even do that? You're not seriously contemplating creating a Y-shaped extension cord with two 5-15P plugs that are then wired such that their respective hots go to each side of a 5-15R receptacle are you?
This is called a "suicide cord" for a very good reason. If the outlets you happen to plug it into aren't on separate circuits it will immediately create a phase-to-phase short. That is virtually guaranteed to damage equipment or start a fire.
Ok, I'm curious. Why would it be a problem if you short together two hots that are on the same phase? They would be at the same or nearly at the same potential, so the output at the 240V outlet would be net ~0 V.
The Y cord would be two 5-15P plugs and one 6-15R. The hot from each plug goes to the hots of the 6-15R. The neutrals are left out and the ground is connected through.
I think the suicide cord you are referring to is a 5-15P to 5-15P cord, which is a bad idea because the plugs are energized as soon as you plug in one side. In this Y cord, the 5-15P plugs would not be energized as long as the 6-15R was connected LAST, after the 5-15P plugs are both in.
You are correct, it would not create a phase-to-phase short. In my head I was thinking something different. The neutrals are not connected, and the hots are on separate pins, so no circuit is formed until a device is plugged into the 5-15R (or 6-15R).
That actually makes me feel better.
However, there are other issues.
1) We still have the risk that someone could plug a 120V device into the 5-15R at the end of the extension cord.
2) This setup will not work with GFCI outlets, as they will trip when they see no current on the neutral. Furthermore, most modern homes now have the GFCI protection at the circuit breaker instead of the outlet, so there are fewer and fewer non-GFCI outlets that you can use this for. (The Quick 220 has the same problem).
3) As n2mb_racing said, if the 240V device is plugged into the 5-15R receptacle before both 5-15P plugs are plugged into outlets, then the exposed pins on the unconnected 5-15P will be energized. Obviously this is a hazard.
4) You don't have any verification that the outlets are wired correctly. It is quite common for a 5-15R receptacle to be wired backwards, i.e. neutral and hot reversed. If one of the outlets is like this, you won't get the 240V at the 5-15R end of the extension cord.
5) If one of the 5-15 plugs is live, and the other one is dead because the breaker is turned off, the dead plug will be fed with 120V from the other plug through the device. If the breaker was turned off because someone was working on that circuit, they are now exposed to live electricity inadvertently. Similarly, if there are devices on that circuit, they will now be in series with the load on the 5-15R end of the extension cord, resulting in partial voltage to all devices, which could damage them.
In short, I still think it's a bad idea.
And using a dryer outlet with a 6-50 adapter and 6-50 extension (with amps dialed down to 24) seems like a better option if fast charging is needed.
You may be interested to know, others have verified that cutting the neutral pin off of your 14-30 or 14-50 connector will make it work on both outlets, obviously keeping in mind to remember to set the amperage lower where necessary.That's what I do for out-of-the-way locations that have no other charging options. I have 10-30 -> 14-50 and 14-30 -> 14-50 adapters for charging from dryer outlets. Just make sure to turn the amps down to 24A in the car.
Agreed, 240 in a 120V outlet in the wall is a bad idea.
A NEMA 6-15 to 5-15 adapter is a much less bad idea. Especially if it is well labeled and kept with the car...
Agreed. I said that earlier. That's what I'm using now. 6-20 outlet and 6-20 UMC plug for one car and 14-50 for the other.Since the native Tesla NEMA 6-15 and 6-20 adapters are available for a very reasonable price, I see no reason to use the less bad idea.