So I am very concerned about installing a 30a charging setup (24a) on a 60a service (that is a tiny service!).
- Each unit was designed to have an electric range oven appliance. There is a NEMA 10-50 plug and 50 A breaker.
In my case I only use a microwave on one phase and a fridge on the other phase.
Also, the wiring in that building looks very old. I don’t think I would want any liability for touching that.
- Each unit main feeder uses aluminium Romex, you are right, this is a concern, I would prefer copper which is nicer to work with.
Even though you are not planning to go over 60 amps of use, you are still impacting the buildings load calculations.
- The EV charging will be performed during off pick hours (11 pm - 6 pm) using the
PG&E Electric EV rate plans.
If everyone did what you did it is virtually guaranteed that the main service would be overloaded
The current installation allows me to use my own meter. if in the future there is a demand for a larger number of vehicles,
there is a a charging service called
PG&E's EV Charge Network program providing the installation of EV charging stations
and
PG&E will install a new feeder from the street in this case.
(the point being that there is over subscription going on based on some formula from decades ago about average consumption
- modern living has likely changed this a lot).
- About the typical actual consumption compared to 'decades ago' typical consumption, I would say that
incandescence light have been replaced by LED, TV tube have been replaced by LED screen,
desktop have been replaced by laptops, and oven range have been generally replaced by microwave...
- My typical household usage is about 300 kWh monthly, so about 10 kWh daily, so mostly lightning (LED), laptops,
and cooking need. Supposing 10 hours full activity, 10 kWh on two 120 V phases is like 4 A average on each phase,
peak load would be when microwave or fridge are used, about 12 A for few minutes at a time on each phase.
But barring the above, I actually question whether you need a sub panel in the garage at all.
I wanted to be able to de-energize the UMC feeder from the main breaker in case there was some maintenance to be performed, without having to disconnect the main breaker. Also, if I was moving out, a new tenant might not be willing to have a plug to be use by someone else..
If your main breaker is 60a, and you tap off that feed with 6awg copper in conduit and then go to a fused disconnect by the car fused at 30a I think that might be legal...
The #6 awg copper in conduit is good to 60a, so I don’t think the “tap” distance rules apply. It may drastically simplify your install.
But this is beyond my level of knowledge, so take it with a grain of salt and check with a professional.
Thank you for your comments. Also, I am only installing the hardware, an electrician will review and activate the system.
If there is some overload capacity issue, I could use a different UMC plug, such as the Tesla 240 V NEMA 6-20 (16 A)
or the 240 V NEMA 6-15 (12 A) instead of the NEMA 14-30 (24 A).
Also, I would recommend THHN in conduit, not NM cable (Romex).
And why not use flex conduit for some of this?
While I am not a fan of it for long distances, it makes all the sense on the world for short runs with weird bends and angles.
So going from your junction box to your main panel may be a good use case.
Work in progress, thank you for the advice.
Indeed I made some progress over the weekend and used MC (Metal Clad) AWG 6 from the master panel to the Junction box.
I was also able simplify and make a nicer EMT raceway curb for the branch going toward the UMC subpanel.
So with the existing Aluminium Romex, there are now three types of wires connected to the junction box.