qdeathstar
Completely Serious
i’m looking at your panel. i think you would have no issue installing a 30 amp circuit for the EV charger. The 240v breakers in there appear to be your air handler and air conditioning compressor. Even though the air handler says 20 amps, it probably only draws 1-2 amps since all it is doing is running a fan to pull air through coils. The AC compressor probably draws around 20 amps when it running worst case, possibly less. You can find out exactly by looking for the FLA marking on the AC. The rest of those circuits probably draw around 20 amps on each phase.
That leaves you with about 20 amps of head room on your service, even with the AC running. The 30 amp circuit will draw around 24 amps... So a little tight, but doable.
Since bryant breakers are no longer manufactured you can get a breaker like this that will fit in your panel.
https://www.amazon.com/Cutler-Hammer-BQ230220-Circuit-Breaker/dp/B00N4Q6VQE
Then it’s just a matter of getting from A to B.
That leaves you with about 20 amps of head room on your service, even with the AC running. The 30 amp circuit will draw around 24 amps... So a little tight, but doable.
Since bryant breakers are no longer manufactured you can get a breaker like this that will fit in your panel.
https://www.amazon.com/Cutler-Hammer-BQ230220-Circuit-Breaker/dp/B00N4Q6VQE
Then it’s just a matter of getting from A to B.