Seems like it would be an easier way to go in many cases, potentially eliminating the need for panel upgrades, 120% rule, etc. I've seen it mentioned a few times in this forum but I can't find a clear answer to this yes or no question.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
I'm hoping that National Grid (NY) approves the B-U Switch quickly, since I've been here with one sitting in a box waiting for over a month now...As pointed out above the backup switch is the slick solution, and hopefully, it will be accepted soon.
Last time PGE approved something like this it took about 18 months.I'm hoping that National Grid (NY) approves the B-U Switch quickly, since I've been here with one sitting in a box waiting for over a month now...
The Backup Gateway is set up to hold a main breaker, which can be the service disconnectTesla does not allow PV plus Powerwall on a line side tap.
Tesla has a new Backup Switch that is a meter adapter ring mounted between the meter and its socket. It's not a line-side tap; instead, it is a grid isolation device (a relay) that is controlled by a low-voltage cable to the Powerwall+. That allows whole-house backup to be implemented just by connecting the Powerwall+ to the main service panel via circuit breakers. But as far as we know it has not been approved yet by PG&E.
That’s exactly what I want - was that schematic from a real Tesla system? What state/country?Yes they support line side tap, maybe region/utility specific. Will need the back up gateway 2 and not the meter back up switch socket
Again, what does your meter look like? If it's in a box with breakers as is common in California, doing what the diagram shows is much more expensive than other options. You'd need to get your service disconnected, that meter main box removed, and a new meter-only enclosure installed. Plus a subpanel if your meter main has distribution breakers. And if the meter main is recessed, your siding repaired.That’s exactly what I want - was that schematic from a real Tesla system? What state/country?
Here's what I've got now:Again, what does your meter look like? If it's in a box with breakers as is common in California, doing what the diagram shows is much more expensive than other options. You'd need to get your service disconnected, that meter main box removed, and a new meter-only enclosure installed. Plus a subpanel if your meter main has distribution breakers. And if the meter main is recessed, your siding repaired.
The only easy way you get exactly that is with the Backup switch. I could see you passing inspection easily with the existing panel, with existing violations. Often if it was overlooked once, it will be overlooked again, especially in PGHere's what I've got now:
View attachment 690274
The house was rebuilt from the foundation up 2 years ago (I bought it a year ago). They generally did a fantastic job, though I can't think of a crappier 200A panel choice. They also violated two of the panel's specs - the panel supports a maximum of one 100A breaker, which has to be put in the lowest position. As you can see they installed a 120A breaker 2 positions above the lowest position. So I will need a new panel to pass inspection.
Anyway, it's a nice, new house, so I want to keep the wiring as clean and minimal as possible. Cost is not my #1 priority. I'm trying to avoid what Tesla did at my previous house (keeping the original main service panel & meter, adding a big junction box, adding an additional load center box, and running conduit everywhere).
Ideally I'd like to keep the loads where they are (so no need to splice all my wires in a new junction box and add an additional load box and deal with all the stucco and possible interior wall work that would entail).
(The boxes and conduit for the Powerwalls, solar, and gateway on the wall around the corner can be laid out cleanly - I'm not worried about that part.)
So what I'm trying to figure out is how to come closest to this dream. As far as I can tell, you can't buy panels that have the meter isolated from the breaker bus (though that would be amazingly easy to do and it seems like it would be a great solution for a lot of solar installations).
Also, this is a 12kW/3 Powerwall install that Tesla signed off on (pending me upgrading the panel) 6 months ago. My goal is to get this work done by a local electrician before Tesla is ready to do their install.
Knowing that elegance is more important than cost, does anyone have any recommendations?
Cheers!
You'll still need to replace your current service panel, unless you are OK with having only 100A of load backed up behind the Gateway, with the rest of the loads not more than 70A individually, and your building department allows the early recognition of Powerwall as a Power Control System that can be configured to limit exports to 80A continuously (since you will have more than 100A * 80% of inverters behind your Gateway).OMG, I finally caught up enough to see what this new Tesla "Backup Switch" is all about. Yes, that's exactly what I want. it gets (PG&E?) (CA?) approved soon. Thanks for the detailed info!
Yes it's the Tesla engineering drawing "01" "3 lines diagram" IL will county but it's not the city here than the county that permitThat’s exactly what I want - was that schematic from a real Tesla system? What state/country?
All the new CSED I have seen have factory-installed and listed conductors certainly from the meter to the main breaker, and usually from the main breaker to the distribution bus lugs.Another possibility would be a new meter/main/distribution that has wire type conductors from the meter to the main breaker that the manufacturer says can be field modified. Not sure if such a thing exists. And then you'd need to mount your Backup Gateway right next to your meter, as it would have a main breaker that is your new service disconnect. A definitely available alternative along these lines is a separate meter enclosure and main breaker panel plus the Backup Gateway, and perhaps having them all surface mounted would look better than a mixture of flush and surface mounted (since the Gateway can't be flush mounted to my knowledge).
Cheers, Wayne
[CSED = Combination Service Entrance Device, a term for meter/main/distribution in one enclosure.]All the new CSED I have seen have factory-installed and listed conductors certainly from the meter to the main breaker, and usually from the main breaker to the distribution bus lugs.
I get meter, but what's the distinction between main and distribution? I could see bus and breakers, but you really couldn't have one without the other, right?[CSED = Combination Service Entrance Device, a term for meter/main/distribution in one enclosure.]
Wire bending room is the number one thing that makes all of this difficult. The only successful field evaluations I have done are turning a CSED into a Meter socket enclosure, and UL certifying a line side tap to factory conductors inside a CSED. The rest is just theoretical, and not the KISS way to deal with this. The good options are outlined above.[CSED = Combination Service Entrance Device, a term for meter/main/distribution in one enclosure.]
One difficulty that I imagine that could be encountered when trying to replace factory installed conductors in a CSED with field wiring is that the manufacturer may have used smaller wires or tighter bends in the wire than the NEC would allow. So you might be left with inadequate bending space or needing to replace lugs to accommodate a larger wire. [Zero first hand experience on these possible issues.]
Also, if you intercept conductors from the main breaker/service disconnect to the gpanelboard main lugs, and route them to the Backup Gateway to provide whole house backup, you'll need to add another main breaker to protect the panelboard bus, which probably means another enclosure. If you are able to intercept the service conductors from the meter to the main breaker/service disconnect, then you can use the space for a line side breaker in the Backup Gateway to install a new service disconnect breaker there, and use the CSED main breaker to protect the panelboard bus.
But certainly I agree that the ability to do some of the above would be a nice option to have when dealing with adding the Backup Gateway to a premises with a CSED.
Cheers, Wayne