If "them" = meter/mains or meter/main/distribution panels, I'm not sure which post of mine you are referring to. The 2020 NEC has potentially two new requirements that bear on this, the first of which I mentioned recently (not sure which thread it was):Yes, as far as I know as well, it is a regional thing. I have only seen them in the West, though from the post by @wwhitney, there will be more of them across the country per the 2020 NEC. Personally, I always liked having the main service panel indoors, though I can see for fire safety reasons why the fire department might want it outside.
1) A panel supplied by service conductors will need to have a main breaker. So the arrangement of "meter -- MLO panel -- multiple service disconnects in one panel" will no longer be allowed. One could instead do "meter -- gutter with multiple taps -- multiple enclosures, each with a single service disconnect". Not likely to impact residential service design much, as a single service panel is typical for residential.
2) (New) residential services will be required to have an exterior "emergency" disconnect. This could be the actual service disconnect, or an additional upstream disconnect labeled "not service equipment". The hardware is the same, the question is whether the EGC-neutral bond is in the enclosure, meaning the EGC system originates there, or not.
Cheers, Wayne