Thanks for your reply. Yes, I plan to make the connection inside a receptacle box behind the dryer.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
The enclosure for the NEMA 14-50 is tricky. The TESLA mobile connector is about 6” long. Most electricians will just install a standard outdoor electrical outlet with a weather proof cover. Unfortunately this will not satisfy the “in-use” code. This code states that if an electrical appliance is plugged in outside the plug must be completely sealed when in use. The standard weather proof cover will not close all the way when the 6” TESLA cord is plugged in. When I install these outlets outside I modify a NEMA 3R cabinet to accepted a NEMA 14-50 outlet and be completely closed when in use. The cabinet is even lockable.
Is he correct about the "in use" code (NEC?). Does that mean if I do it myself I also need to modify the NEMA 3R enclosure?
For the last group of electricians, aren't they risking their license or some punishment if he does the work without a permit?
FlasherZ: In your FAQ you warn against a 6-20 to 14-50 adapter for folks with a 20A 240V air conditioner outlet. I agree 6-20 to 14-50 is dangerous because of overdraw if someone forgets to dial down amps, but what about building a 6-20 to 5-20 adapter? Though you should make it VERY CLEAR that the 5-20 receptacle is NOT to be used as a 120V receptacle, this seems like a good solution to me. The UMC will take the 240V even though the 5-20 adapter is intended for 120, and the wired resistor will indicate to it a breaker setting of 20A. Thus you get all of the benefit of the 240/20 wiring without risk of overdraw. What do you think of this?
You don't need to build it. EVSEadapters.com sells one.FlasherZ: In your FAQ you warn against a 6-20 to 14-50 adapter for folks with a 20A 240V air conditioner outlet. I agree 6-20 to 14-50 is dangerous because of overdraw if someone forgets to dial down amps, but what about building a 6-20 to 5-20 adapter? Though you should make it VERY CLEAR that the 5-20 receptacle is NOT to be used as a 120V receptacle, this seems like a good solution to me. The UMC will take the 240V even though the 5-20 adapter is intended for 120, and the wired resistor will indicate to it a breaker setting of 20A. Thus you get all of the benefit of the 240/20 wiring without risk of overdraw. What do you think of this?
Flasher, thank you for providing this great FAQ resource to the TMC members!
After reading the thread, I am ready to install a HPWC in my garage and have a few questions:
1. I only have a 240V/30 Amp circuit available, so the electrician has recommended 24 Amp charging?
2. He recommended running 10 Awg wire to the new HPWC which is a 50 foot run in the garage?
3. Would you recommend running the new wires in a conduit or go with cheaper NM cable?
4. Any other suggestions? I want to minimize the cost and can live with 17Mph charging.
Thanks
You don't have to use that 30 amp breaker. You can swap it out for a bigger breaker. Not sure why you wouldn't at least use a 50 amp breaker.
I should have mentioned that the existing 30A circuit to the Dryer uses 10 Awg wire.
I am planning to extend the unused Dryer circuit to the garage to service the HPWC.
My answers are based upon what you have written here, plus - based on your clarification - that you're going to extend the dryer circuit from your laundry room to the garage, instead of running new wire all the way from the panel. Based on that assumption:
1) yes, on a Wall Connector configured for 30A, the charge current will be 24A; this is because a circuit must be sized at 125% of the offered load. 24 * 125% = 30A.
2) yes, a 30A circuit requires a #10 copper conductor
3) this can vary by code... if running inside the walls, NM cable is just fine unless code prohibits it (Chicagoland and some NY localities). If running on the surface of walls, NM cable must be protected from "physical damage", a term interpreted by AHJ's. The most common interpretation requires the NM cable be encased in an EMT sleeve and fittings anywhere below a line drawn 7' above the floor surface. So if your plan is to have the cable run on the surface of walls, you'll likely use some form of conduit anyway to protect it from damage.
The plan you are envisioning is likely the lowest-cost approach. Your connection to the existing 30A circuit must be made inside a junction box or wall box with an appropriate cover -- will you be making it inside a receptacle box behind the dryer?
What is the maximum bend radius of a PVC conduit for three #6 conductors and a ground wire (for a NEMA 14-50 outlet), and 3 #2 conductors and a ground wire (for HPWC), respectively, such that the conductors can be pulled? The conduit run is 50 feet.
Assuming copper...
sch 40 or sch 80? Sch 40 requires 3/4" for 3x#6+1x#10, while sch 80 requires 1" for the same. NEC 352.22 says the internal diameter must not be compromised, and points you at table 2 in chapter 9. For a 3/4" conduit, maximum radius is 5"; for 1", it's 6" (from table 2).sch 80 is required where inspector would require protection from physical damage.
For HPWC, you only need 2 #3's and a #6 ground; that requires 1" conduit regardless of sch 40 or 80, so 6" bend radius; same if you go to 2x#2+1x#6. If you still want 3x#2's+#6 anyway, that would require 1 1/4", maximum bend radius 8" from table 2.
Sum of bend angles may not exceed 360 degrees without pullboxes.
Conduit fill calculator I use: Raceway Fill Calculator