All right. So, this feels a little weird, but bear with me here. Starting from the top:
- In the main breaker panel, there's a duplex 60A breaker that provides (at most) 48A of continuous load. Two hots, a safety ground, and maybe a neutral leave the breaker box.
- Now, on my Gen 2 WC, the two hots, neutral, and ground hit the WC and there it stops. If I add another Gen 2 WC, I bolt on another pair of hots, a neutral (not sure about the neutral, got to go dig out the manual), and a ground and connect that to the next Gen 2 WC in line.
- On the Gen 3 WC, the 60A service wire from the breaker panel shows up and goes into a sub-panel that is mounted next to or near the first Gen 3 WC. The sub-panel accepts that 60A service feed and connects said feed to two (2) each 60A breakers.
- Each of the 60A service feeds from those two (2) 60A breakers in the sub-panel then go to a Gen 3 WC.
So: For current to get to a Gen 3 WC in case #3 above, it first goes through a 60A breaker on the main panel, then one of the two 60A breakers in the sub-panel, and then to the associated Gen 3 WC?
Feels weird, somehow. But I guess in a Standard House it's not unusual for current to go through the Main Breaker in the main, then through innumerable breakers on each circuit, and so on.
And total current in the feed back to the main breaker panel never exceeds 48A, right?