The "dial" is in "80%" units. So just to not confuse the OP, you don't set the dial to the Breaker Size. You set it to 80% of the Breaker size (most of the time). Some breakers can be "rounded up" by 5 Amps. So the dial is set to 80% of the Minimum of the Breaker Size or Wire Capacity.
I disagree. Set the HPWC dial to the circuit breaker/ampacity rating. The HPWC will limit charging to 80% of the rating. 40 Amp breaker with proper wire gauge? Set dial to 6. HPWC will only allow 32 Amps.
I had our electrician install 100 Amp breaker in the panel - he verified it was within panel limits. Then had crew run 2-gauge copper to a new sub-panel near the driveway. 100 Amp breaker in the subpanel, 2-gauge copper to the HPWC. That gives us options if we want to install additional HPWC or other charging arrangement. Subpanel with breaker counts as cutoff since it is visible from HPWC.
Electrician originally planned to use aluminum cable between main panel and subpanel. I told him I would gladly pay the premium for copper. Lower resistance, more acceptable to future home buyer.
Also had the electrician run shielded twisted pair from HPWC to a reel in the ceiling. That will allow multiple HPWC to share the 100 Amp circuit.
HPWC dial set for 100 Amp service. Our Model S 100D gets its full 72 Amps. My friend's S 85D with dual chargers can pull a solid 80 Amps. The copper cable is slightly warm to the touch. Wife's P3D- gets its 48 Amps.
Every month or two there's a situation where relatively fast home charging makes life easier. Mids-afternoon last Saturday we decided to go to a distant barbecue place for dinner. I connected wife's 3 to HPWC and started charging. The car added enough range that we could make the trip without anxiety.
Live near Philadelphia, it's a Supercharger desert. There is no option to, "Stop by the SuperCharger for 20 minutes to add some range."