Here is my sub-panel status: 125A max panel size, main cut off breaker for sub panel is 90A.
1. Do I have option for 30A addition ?
- The breakers will need to shuffle to add room for dual-30A : move the bottom 20A to the right with corresponding wiring ?
- The main wires, #1/0 wiring size, correct ?
There are some rules, like don't feed a 125A rated panel with breaker larger than 125A, and don't load this 90A supplied subpanel with more than 72A for more than 3 hours. But otherwise "capacity" is generally subjective and note that high-power devices like the oven, dryer, air conditioner, etc. likely only use around half of their breaker-rating.
I'd replace those 4 15A breakers at the bottom right with a pair of tandem breakers and then add a 60A breaker for your wall charger if conduit is preferred, or 50A if Romex is preferred. Then if you find that charging at 48A (conduit) or 40A (Romex) causes trouble when using the oven or whatever, either change your habits or dial it down to the next level in the charger.
Of course this all gets a lot more complicated, expensive, and unreliable if you're thinking about using an outlet instead of a direct-wired wall charger, and maybe you are, considering the topic of this thread. If so, you'd want a 50A GFCI breaker and you lose the ability to limit the charge rate right at the charger, but still have the ability to configure the car for location-based charge rate limiting.
And yes, 1/0 wiring is fine for 90A service, even the next smaller size works in most cases.