huntjo
Member
View attachment 45509My electrician installed with the cable through the holder. Not aware that it critical... I do like the HPWC.
Cute dog!!
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
View attachment 45509My electrician installed with the cable through the holder. Not aware that it critical... I do like the HPWC.
Got a call this AM that the electrical inspector was coming out to inspect the HPWC install. Gave me a whopping 3 hours notice and I can't get home from work but thankfully the wife is home to let him into the garage. All I've gotten over text so far from my wife:
"This guy has never even seen one of these let alone inspected one."
"He's got the instruction manual out trying to figure out how to open it up."
"He's shocked that it is 100Amps"
"He keeps asking me questions and I obviously have NO idea."
Oh boy...not feeling very good about this...hopefully he can't screw it up!
"He's shocked that it is 100Amps"
In the future I may upgrade to a 90A breaker since the cable run is only about 8 feet. What size of wire does that require?
OUCH!!! :scared: $3600???!!! That's more than 10 times what I paid. I'm sure there must have been extenuating circumstances.
I don't want to rain on the parade either, but that is REALLY high for that... and I'm not even sure that is a legal install. Can you take a pic of the white writing on the supply wiring - i zoomed in but can't read it.
Well, after much stressing and even more waiting, my HPWC was finally installed on Monday! It only cost a little over $3600. :scared:
Hopefully, it will actually work when I get my car in a couple weeks. My electrician did good work but he doesn't read instructions. I had to inform him about the HPWC's internal dip switches and how to set them appropriately (I only had room for a 70A breaker). Also had to perform the Test Mode check myself after they left. All good there, fortunately.
In the future I may upgrade to a 90A breaker since the cable run is only about 8 feet. What size of wire does that require?
OUCH!!! :scared: $3600???!!! That's more than 10 times what I paid. I'm sure there must have been extenuating circumstances.
90A breaker requires #3 assuming breakers with termination rating 75 degC. If you have room in the panel's load calculation, with the same wire size you could go straight to 100A rather than 90A.
... and I'm not even sure that is a legal install. Can you take a pic of the white writing on the supply wiring - i zoomed in but can't read it.
I would LOVE that but the garage service is only 100A and I have to share it with a 20kW heater. Might technically be doable but the electrician wouldn't okay it for install.
20 kW is 83A @ 240V and that's a pretty serious load (my house's emergency heat strips are only 12.5 kW for the entire home!)... 20A perhaps? In that case, he'd probably require you use the 80A setting which would allow for 64A charging and would require #4 cable, if your feeder is 100A.
That TECK90 cable is incredibly expensive. I'm surprised he didn't use standard conduit and THHN wire.
Reviving this thread because I wanted to post my cost to have HPWC installed. I added dual chargers at the last minute. It was an expensive decision. I know I could still go with the NEMA outlet and not utilize high charge rates at home, but...
I'm going with option B, but it has added significant expense to my car and was sort of a last minute decision on stuff I probably didn't need and don't know if it's really worth it. $1500 twin chargers + ~$100 added tax to car + $1200 HPWC + $1926 Electrical work = $4726.
Reviving this thread because I wanted to post my cost to have HPWC installed. I added dual chargers at the last minute. It was an expensive decision. I know I could still go with the NEMA outlet and not utilize high charge rates at home, but...
Anyway my quote is $1426 for option A which involves cutting a hole in an interior plaster wall to run the line to the ceiling and then to the garage (Note: as luck has it, the breaker box is as far away from the garage as you can get in my house). Then I'd have to have the wall repaired and repainted. Plaster guy says he'd have to do the whole wall for it to look right with the sand texture. And I just had this area painted not 3 mos ago. This is too much hassle and would probably end up costing more than option B.
Option B is running conduit up the exterior of my house (vinyl siding on the least visible side which already has the electric meter and pool equipment) to the soffit and then through an attic space. Probably a bit of an exterior eyesore. This is $1946.
Electrician says the NEMA would be significantly less both labor and materials because smaller cable is easier to handle and cheaper. I didn't have him give me an exact quote. I'm guessing about half the price or 2/3.
I'm going with option B, but it has added significant expense to my car and was sort of a last minute decision on stuff I probably didn't need and don't know if it's really worth it. $1500 twin chargers + ~$100 added tax to car + $1200 HPWC + $1926 Electrical work = $4726.