I totally agree the lowering came because people have bad wiring, codes not strong enough or clear enough for wiring NEMA 14-50 and people trying to save money on wiring (and home grown "electricians" that connect whatever makes it appear to work).
1. US and Canadian electrical codes have language around ratings for "continuous loads". EVs draw power continuously unlike stoves, dryers or heaters that cycle on and off and provide some time for cooling. That is why they are rated at 80% of the circuit rating.
2. In Canada, and I believe in the US it is common and permissible under code to wire a NEMA 14-50 to a 40 amp breaker with wiring rated for 40 amps. Most, if not all electric stove outlets are wired this way. If you pulled 40 amps continuous on a circuit like this and the breaker didn't trip (as it should) you could end up with overheated wiring. This has nothing to do with shoddy wiring.
From a safety perspective, it makes sense to rate the UMC for "lowest common denominator" situations. Not everyone who uses these things will be as savvy as folks around here and I personally put safety above all else. If you want or need more than 32 amps, simply get a HPWC or other EVSE and hard-wire it in to the rating you desire. Simple.