Trying to get my options without burning my new house down upon move in. I requested the builder put in wiring capable of 60 amps to allow for 48 amp max charging for a hard wire HPWC install later. I may have drives where I come home to near 5% that I would like the flexibility of the extra amperage to make another quick stop within a few hours.
The builder's contractor however installed NM-B 6/3 w/ ground wire, which I've found out is only rated for 55 amps and definitely not the continuous pull. I didn't mind the 6/3 as I understand with the neutral could remove the HPWC and install a 14-50 NEMA outlet later and change the breaker to 50A for other EVs down the line.
What options do I have if I want 48 amps and maintain ability to convert to a 14-50 or 6-50 down the line?
Would the best option is to ask for direct replacement with 4/3 wire?
The other option would be to run #6 THHN/THWN +/- neutral if I wanted ability to convert back to 14-50 down the line correct? Would I need conduit for the #6 if installed behind the sheetrock?
The sheet rock isn't up so the timing is right to make the correct change all behind the walls. The run is only about 15 feet from the breaker.
Any help would be appreciated, I've spent the afternoon trying to find the answer myself and I wasn't able to.
The builder's contractor however installed NM-B 6/3 w/ ground wire, which I've found out is only rated for 55 amps and definitely not the continuous pull. I didn't mind the 6/3 as I understand with the neutral could remove the HPWC and install a 14-50 NEMA outlet later and change the breaker to 50A for other EVs down the line.
What options do I have if I want 48 amps and maintain ability to convert to a 14-50 or 6-50 down the line?
Would the best option is to ask for direct replacement with 4/3 wire?
The other option would be to run #6 THHN/THWN +/- neutral if I wanted ability to convert back to 14-50 down the line correct? Would I need conduit for the #6 if installed behind the sheetrock?
The sheet rock isn't up so the timing is right to make the correct change all behind the walls. The run is only about 15 feet from the breaker.
Any help would be appreciated, I've spent the afternoon trying to find the answer myself and I wasn't able to.