The kVa rating at 480v does not mean that the unit can output a maximum of 350 kW. The input can go as high as 528v and the peak rating is going to be higher than the continuous rating. The cabinets can share the energy through the DC bus at a higher voltage as well, so they can actually exceed 480v and then share that to other cabinets while outputting 400v to the cars connected. Also, kVa to kW is not a 1:1 measurement.
Yeah, yeah kVa isn't 1:1, but in these cases it is close enough. Sure, input voltage could go higher, but all of the utility transformers I have seen them use have been 480v. Sharing power doesn't increase the AC input voltage... So not sure what you are talking about there. Unless there is an extra cabinet with no stalls on it, any sharing steals, the limited, power from another stall.
A common Tesla installation is a 1000kVa, pretty much 1000kW, transformer with 3 cabinets and 12 stalls. So only ~83 kW per stall... Tesla has sized their installations for what makes sense in the real world, not the silly requirements that NEVI has.
And there is still the problem that it is limited to 500v output, and I think that NEVI requires 1000v capabilities... So all the rest doesn't matter.
Edit: Also, the rules only state that 4 stalls need to be 150 kW or higher. An 8 stall site that has at least 4 stalls running at 150 kW passes that rule.
Not if the other 4 stalls are NEVI funded. And as I said states apply restrictions on top, some of which do not allow power sharing at all. Again here is what their guidance says:
This final rule establishes a requirement that each DCFC located along and designed to serve users of designated AFCs must simultaneously deliver up to 150kW, as requested by the EV
Notice it says "each", not the first 4, or at least 4, or anything like that.
We will have to wait to see how the first NEVI funded site Tesla installs is built. My guess is with V4 chargers that we haven't seen yet.