But curious about the voltage drop, all wiring stays cold to the touch (accept from the HPWC to the car, the HPWC whip gets slightly warm at 80 amps). The Copper from the HPWC to Sub Panel in garage is cold, breaker is slightly warm, Aluminum from the Garage to the house is cold. 100 amp breaker for garage in main panel is slightly warm. Main 200 amp house breaker is cold as are the mains.
Sounds good. I will have 4 test points, HPWC, Load Center in Garage, Main Service Entrance into Main Panel, and a Meter thats 15 Ft from the transformer on another structure. I'm going to have someone take a peak at the transformer today and see if they can tell what it's kVa rating is. I do know it's ancient as heck and extremely rusty, so it wouldnt be beyond me that it's under-rated.As FlasherZ said, check Voltages at the various points you can get access to. Ohm's Law: V = I*R. 60 Amps should be fine for your investigation. You can use the App on your phone to turn charging on and off remotely to check Voltage changes with current. Even if other loads are changing, a couple of on/off cycles at each test point should let you see the Delta-V caused by your Delta-I.
Cold to the touch can still cause a Voltage drop if there is very good heat dissipation at that point. The Volt Meter is the test instrument of choice for this problem.
A good puzzle can be a pleasure to solve! Good Luck!!
It's a family business. Install is done properly. I don't do hackjob installs. I don't know everything, and know my limitations, and when I do have questions, I ask. So, I had 2 questions for the most part, one was how exactly they get away with 6AWG from the HPWC to the car, and second was opinions on the voltage drop, which I will be investigating further.
I'm leaning towards transformer as well. asked around today, Apearantly the transformers fuse blows on a yearly basis.... don't even know where to start with that one. will test voltages this weekend and see what I turn up.Yeah, I'd be willing to bet that you're stressing that transformer pretty heavily. Call the PoCo, ask them to consider upgrading as your load is going to increase. If they refuse, bring a few more Teslas and boil the oil out of it so they have to replace it.![]()
Glad I had a good electrician put my HPWC in. Love it. Nice to not have to figure it out. I have messed up my share of things making it work.View attachment 47632
as for bringing more teslas, on May 17, Sandrift is hosting a large tesla get together. already have six model s's, Chevy volt, and three Prius RSVP'd.Yeah, I'd be willing to bet that you're stressing that transformer pretty heavily. Call the PoCo, ask them to consider upgrading as your load is going to increase. If they refuse, bring a few more Teslas and boil the oil out of it so they have to replace it.![]()
Thought I'd update. Checked through everything today. Re-Torqued the lugs on breakers and in the panel's. I am able to sustain 70 amp charging for about a hour before it limits down to 60 amps. 60-65 amps can be sustained no problem. Voltage drop now from no load to 80 amp load goes from 247 down to 229v.
Voltage drop between car (as displayed on the car screen as viewed via the iphone app for ease) and at the main service entrance in the house panel (Supplied by thick as heck 2/0) was only 1-2v at it's worst. I'd say thats fairly good given the distance of wire (25' HPWC cord, 12ish ft from HPWC to Sub-Panel, about 15 ft of Aluminum wire from Sub to main panel).
Now, voltage at a service entrance that is 15 ft from the transformer is 250, when I start charging the car at 80 amps, the voltage at the panel near the transformer dropped to 246.
I attached a picture of the transformer. The only writing on it. Transformer was buzzing a fair bit more then usual. I'm starting to think that its the distance from the transformer to the house is where the big drop is.
I'm going to get my tripod later, their is another info plate on the other side of the transformer, but is about 3x2", and the sun it hitting it just right to make it un-readable.
If it is, your only hope to improve the situation is to up the wire size or run more wire in parallel. I'm sure FlasherZ knows the rules on paralleling wire, but I know it passed code at my house.
75 kVA rated transformer, that's pretty beefy. Good for ~300A or so, seems about right sizing for the loads.
Based on what you're observing at the panel near the transformer, it seems like you're correct. Voltage drop due to transformer would be seen at that panel.
2/0 AL is good for about 130A or so, but distance can cause a drop. Using my handy calculation tables and Ohm's law, a voltage drop of 18V minus 4V at the transformer/service equipment minus 2V from main to car is 12V. Using Ohm's law, 12V @ 40A is a resistance of .3 Ohms (R=E/I) and using typical resistance of 2/0 AL cable (.128 Ohms per kft), this would be a round trip distance of 2.34 Kft or one-way distance of 1.17 Kft from the service entrance to the home panel. Sound about right?
- - - Updated - - -
NEC says parallel conductors may be used when larger than 1/0.
The only aluminum that is used Not counting anything the utility has on the poles is between the house and garage. that is 2awg. everything else is on the poles governed by the utility. The service entrance to all properties is Copper.Look at the write up, he was doing the measurements at 80 Amps, so the distance is down to 585 feet.
2/0 AL sounds a little light for running a business and adding a couple of HPWC's. Hope it's not 500 feet that needs upgrading...at least 2/0 is bigger than 1/0, so you can go in parallel, just keep the lengths the same for good current sharing...
I will be changing over hopefully 2 Electric Stoves/Ovens to Natural Gas giving us 60 more amps to play with.
If you know someone with an IR camera you can check wiring for hotspot quickly and safely that way.
That seems a shame. Making ff infrastructure investment so your electric car charges faster somehow seems contradictory. May want to check you kitchen venting, make sure it effectively vents to outdoors.
Any other way to do that for similar investment? We really need to be shifting AWAY from natural gas...
How often do you guys with dual chargers drive far enough in a day that you need more than 40 amps overnight? That a fairly regular occurrence?
Thought it would be easier if I just drew a picture. Flasher was more right on. At the meter on the house I have the voltage drop yet.
I hope my picture is not too confusing. The voltage drop is happening between the houses meter and the transformer.