Bottom Line:
I tend to see just under 7% total loss.
I could screw with this for the rest of my life and change it by less than 2% if I could change it at all, and there's no ROI in a change that small. If I was looking to tweak it I would run 60 amp capable wiring and test various total efficiencies. I could no doubt reduce "awake" time and, if using a down-rated charge rate like 32 amps or perhaps 40 amps reduce circuit loss. What would the OBC do? Unknown.
Details:
I have two energy monitoring systems in the home. An Enphase monitoring the solar system and energy consumed, and an Emporia Energy Vue Gen 2 again monitoring energy consumed and also individual circuits. For the latter I've evaluated the CT's used and am using only those reporting within .1%. That said any CT system has errors. We can hypothesize, but reaching hard conclusions within a few percent should be taken with some reservation. At the same time considerable time has been spent challenging the monitoring system and I'm pretty confident these are very accurate. Data for your consideration:
1 month old MY3LR.
3-10 charge using Wall Charger@ 24 amp/240v for 75 min
Garage Temp 47f
Wiring loss for the panel to WC circuit is calculated to be 1.04% The Wall Charger has to have its own consumption, and it's own cable loss, but an additional ~2% - 3% seems high to me. I suppose I'm not too pleased overall efficiency is ~7% to the battery, but is what it is, and at least the power has no cost to me.
Finally, how accurate is the power delivered to the cells? No idea, but aside from some small resistance loss it should be very accurate. Will that always translate to matching range? Mostly, but less healthy battery systems should have more pack resistance and therefor less energy actually absorbed by the battery.
Noob though, so WTF do I know?
I tend to see just under 7% total loss.
I could screw with this for the rest of my life and change it by less than 2% if I could change it at all, and there's no ROI in a change that small. If I was looking to tweak it I would run 60 amp capable wiring and test various total efficiencies. I could no doubt reduce "awake" time and, if using a down-rated charge rate like 32 amps or perhaps 40 amps reduce circuit loss. What would the OBC do? Unknown.
Details:
I have two energy monitoring systems in the home. An Enphase monitoring the solar system and energy consumed, and an Emporia Energy Vue Gen 2 again monitoring energy consumed and also individual circuits. For the latter I've evaluated the CT's used and am using only those reporting within .1%. That said any CT system has errors. We can hypothesize, but reaching hard conclusions within a few percent should be taken with some reservation. At the same time considerable time has been spent challenging the monitoring system and I'm pretty confident these are very accurate. Data for your consideration:
1 month old MY3LR.
3-10 charge using Wall Charger@ 24 amp/240v for 75 min
Garage Temp 47f
Tessie reported power consumed: 4.16KW
Panel CT Monitor reported: 4.321KW
Tessie reported added to battery: 4.03KW
Tessie reported efficiency: 97%
Actual: 96.9%
Overall Efficiency: 93.3%
Loss to Wiring/EVSE, etc 3.6%
Line Voltage Variance: 235V - 243V
During this time the doors were open for 10-15 minutes and as I recall the heat pump started. Finally, line voltage variance was a bit high, with a low of 235V.
3-10 charge for 170 minGarage temp 57f
Tessie reported power consumed: 16.34kw
Panel CT Monitor reported: 17.05kw
Tessie reported added to battery: 15.91kw
Tessie reported efficiency: 97%
Actual: 97.3%
Overall Efficiency: 93.3%
Loss to Wiring/EVSE, etc 4%
Line Voltage Variance: 239V - 243V
This final (170 minute) charge terminated at 63%, so the BMS was not limiting anything. Cabin preconditioning would have run during this time for a brief period as well. Is this reported accurately? In other conversation with JCannoe I've been led to believe all conditioning circuits are driven by the HV system and would be captured by the OBC as "delivered to the battery". Meaning "yes, data reported by the BMS/OBC will remain accurate".Wiring loss for the panel to WC circuit is calculated to be 1.04% The Wall Charger has to have its own consumption, and it's own cable loss, but an additional ~2% - 3% seems high to me. I suppose I'm not too pleased overall efficiency is ~7% to the battery, but is what it is, and at least the power has no cost to me.
Finally, how accurate is the power delivered to the cells? No idea, but aside from some small resistance loss it should be very accurate. Will that always translate to matching range? Mostly, but less healthy battery systems should have more pack resistance and therefor less energy actually absorbed by the battery.
Noob though, so WTF do I know?