You keep saying this. There is no "16-20". We have been talking about a 6-20.
A Nema 16-20 requires 2 - 20 amp 120 volt circuits
No, it really isn't. The word "circuit" has its roots from the same source as "circle" for good reason. It is one complete loop. It is
one circuit,
one loop. You connect the breaker on different places on the panel so that it gets a higher voltage potential, but it is still just one loop of wiring on that circuit, and it uses the amount of current that it says--not double.
But I am willing to bet that if the house has an Oven, Hot Water Tank, Air Conditioner and Dryer at 240 volts that there is any possible way that there is additional space (power wise - there maybe physical slots which mean nothing to total load).
Yeah, we already covered all of this by page 2. Load calculation already showed that he only had 10A to spare, so he needs to use the DCC-9 to manage the load.
Here is the Electrical Code:
624.14 Electric vehicle charging loads shall be considered to be continuous loads. Where an automatic load management system is used, the maximum electric vehicle supply equipment load on a service or feeder shall be the maximum load permitted by the automatic load management system.
The definition of a Continuous Load is any load that is expected to continue 3 hours or more...
Yes, I am very well aware of that section of code. And further, that in the newer section 625, which was added in NEC 2017, that it just defines ALL EV charging as continuous loads, regardless.
So, even though you can lower the current draw of a Tesla Wall Conector, you must do all calculations based on its maximum output.
With Continuous Load the Breakers must be 125% of the maximum load.
No, that is not what that means at all. This isn't about "turning it down a little" from how it's installed. That is an internal configuration switch which is set to
define the load of the appliance. You don't have to treat the wall connectors as always 100A circuits or 60A circuits because that was what they are built to be capable of. If you are putting it on a 40A circuit and configuring it to BE a 40A circuit device, then that is what you use for the load calculation. It's a 32A continuous, requiring a 40A circuit.
With an Electrical Car Charger as a example a 15 Amp draw would require a 20 Amp Circui, etc...
Yeah, all EVSEs are already built to comply with that type of limitation all the time. People just need to make sure they are clear about what they are reading to know what the current number is referring to. The device may be talking about either what current it supplies or what level of circuit it is supposed to be installed on, and obviously those numbers will be different.