Code clarification: The breaker has to be sized for the LOWEST rating of any wire or device in the circuit (exception: 15 amp outlets on a 20 amp circuit, since you can't plug in a 20 amp appliance to a 15 amp outlet). So this means that yes, you can put a 14-50 outlet on a circuit that is protected by a 30 amp breaker. Just like you can run 6 gauge wire to a 20 amp outlet it's OK by code, but you have to have no more than a 20 amp breaker protecting the circuit. Also, code says that if you are going to draw continuously for 3 hours or more you have to de-rate by 20%. So even if everything in the circuit is rated for 30 amps, you can't draw more than 24 amps, by code, for more than 3 hours. So set your car to charge at 24 amps at that location. If you want 30 amps and the car will be charged at that rate in less than 3 hours, it's OK to bump the charge rate up to 30 amps. There's nothing stopping you from drawing 30 amps for 10 hours straight since code doesn't make you put in a 24 amp breaker, but you'd still be violating code.
Per code, you are not allowed to put a 30 amp breaker wired up to a NEMA 14-50. Code mandates that the breaker match the outlet, period. The only exceptions to that are the 50 amp outlets (14-50, 6-50, etc), which allows a 40 amp, but NOT a 30A breaker, and also the 15/20A 120V outlets, since those are intended for multi-drop branch circuits. While I agree it will be safe (assuming you don't repeatedly trip the breaker, and only uses 24A max), it isn't up to code and would fail an inspection, regardless of the wire backing it.