No. Please read the code. You are incorrect.
240.4(B)
This is pointless conversation however, since 6-3 NM cannot provide 48 Amps.
While 4/2 NM is the easy solution, 6 gauge THHN, as the post above indicated, is fine for a 60 amp breaker. You need to look at the 90C column of the table.