davewill
What matters is what amperage is shown AFTER you plug in. Before you plug in, the car will show 48a as a max because it doesn't know what the amperage of the wall connector is.
Exactly this. Major source of confusion and so few people understand it.What matters is what amperage is shown AFTER you plug in. Before you plug in, the car will show 48a as a max because it doesn't know what the amperage of the wall connector is.
Thanks guys. I tested today and first went in to my phone app and changed it from 48 to 40. Charged for 2.5 hours without tripping breaker. Although I did notice the breaker was pretty hot. An hour later went back into my app and it wants to start at 48. Assuming it's an app issue but now I know what to do (or not to do). Thanks for all your input! I have learned a bit about electricity but think I'll stay away from it as much as possible.
Not a good solution for a daily charging solution. The setting in the car is prone to being forgotten or ignored. Then you'll trip the breaker again. PLEASE, make the effort to correctly provision the wall connector so that you CAN'T charge at the wrong amperage.Tx for the feedback. I set it on the car and it does just that now. Everything good. Learning processes......
I have already gone through the provisioning and it was set correctly. As it is I'm no longer having any issue. Thanks for the feedback!Not a good solution for a daily charging solution. The setting in the car is prone to being forgotten or ignored. Then you'll trip the breaker again. PLEASE, make the effort to correctly provision the wall connector so that you CAN'T charge at the wrong amperage.
Really? You can run 2 6ga thhn and a 10ga thhn ground in 1/2 emt. Interestingly, you can't run just 2 6ga thhn but adding a third conductor allows you higher fill %.There us something wrong. 8 gauge wire shouldn’t be installed in 1/2 emt. The evse isn’t commissioned for a 50 amp breaker, it is commissioned for a 60 amp breaker. You would need #6 thhn not 6/2 romex.
Once the breaker got heat soaked it was more likely yo trip. If you don’t use it for an hr and give it time to cool off You should be able to charge at 40 amps unless the electrician didn’t properly tighten the lugs in the breaker or your panels buss bar is damaged.
You are allowed three 8 gauge THHN in 1/2” EMT, so there is nothing wrong with the choice of conduit if he used 8 gauge,
Echoing others who said the problem is that EVSE didn’t get commissioned properly. It needs to be commissioned via an app to set it to a 50A breaker installation.
Also echoing others who said the electrician probably screwed up by not using 6 gauge and a 60A breaker to maximize your charging speed.
If you have changed nothing on the HPWC then it is still incorrect as others have stated. Changing the settings in the car does not fix the issues with the HPWC. Can you post a picture of your screen while the car is charging at home? This will help to ensure the HPWC is working properly.I have already gone through the provisioning and it was set correctly. As it is I'm no longer having any issue. Thanks for the feedback!
I am reasonably confident that Tesla v3 HPWC (current model) setup dialog uses breaker rating. This information is easiest to find - it’s visible when you open the electrical panel door.I've never commissioned a HPWC, it's possible that the use interface is confusing.
Was your electrician licensed?Thanks everyone for the excellent feedback. I do have the electrician coming back out so I'll see what he says. He will double check all screws for tightness and bring a spare breaker. I went back through commissioning and it was/is set for 50 amp breaker so that part is good. I will set the phone app to 40 now and see what happens. I did see thhn on the wires in the panel but not sure if it's 8 or 6 but pretty sure it's 8. The conduit has 3 90 degree bends. Hopefully I'll post what fixes the issue.
Regarding the 2 versus 3 conductor fill rates, it’s due to they shape of each conductor. The third fits in differently than the second.Really? You can run 2 6ga thhn and a 10ga thhn ground in 1/2 emt. Interestingly, you can't run just 2 6ga thhn but adding a third conductor allows you higher fill %.
Here is the concern. With the car set at 48A and the HPWC attempting to charge at 48A, some issue is being magnified and causing the breaker to trip. Setting the car to 40A brings this issue to within spec and charging continues but there is still an issue that could cause problems in the future.
I've been thinking about retightening the connections on my v2 WC. Curious as to what you saw with voltage and heat at breaker with your v2 chargers that prompted you to tighten the connections. My voltage hovers around 238v and I've gotten temps at the breaker of up to 127f in an enclosed garage with ambient temps in the high 80's. With garage open temps are about 10 degrees less thanks to airflow.In very case I had to tighten wire connections after the electrician left to reduce voltage drop and circuit breaker heat during full-capacity charging - 80 Amps for the v2’s; 48 Amps for the ChargePoint.
I can’t remember the temperatures. I removed the panel cover; started car charging at full draw; waited 5 minutes then measured temperature with a probe. If it seemed high I stopped charging; turned off breaker and then tightened the connection.I've been thinking about retightening the connections on my v2 WC.
Also check the connection at the HPWC end. Our daughter and her husband had to replace their v2 HPWC. The electrician’s “B Team” hadn’t tightened the termination to spec. They didn’t realize it, but over time the overheated connection fried the HPWC electronics.
What do you mean by the shape and the third fits in differently than the second? Are there conductors that aren’t round? And fill % is about cross section so the shape doesn’t matter. Whether a stranded wire is round or flattened oval, it’ll still have the same cross section a fill %. 2x 6ga thhn are going to fit the same way in 1/2 emt whether another conductor is there or not. Having a third conductor will help with pulling through bends but it doesn’t change the shape and fit of the 2x 6ga conductors.Regarding the 2 versus 3 conductor fill rates, it’s due to they shape of each conductor. The third fits in differently than the second.
Also, just because you can doesn’t mean you should. Electricians that pull wires all day will install wherever works best for them (above minimum allowed sizes). I.e. I have 1” EMT run to my 6awg R90 setup. There are a few bends in there.
The HPWC isn't commissioned properly. It shouldn't even be trying 48 amps. That said, it should be able to run at 48 amps for at least a little while(minutes) before the circuit breaker trips. You should not and can not rely on the car/app setting to keep the rate lower than 48 amps.
There is still a problem at the breaker. Either the breaker itself is defective or the connections are bad. Connection(s) because there's the obvious ones you screw in very tightly and the less obvious ones that clip onto the bus bars. When panels get old, their bus bars can get corroded and bad connections cause heat. Heat is one of the criteria that the breaker uses to trip.
You should set everything to max and it should automatically switch to 40A when actually charging. If it doesn’t it’s not set up right. User should not be able to charge over the hard configured limit, ever if wall connector is set correctly.Tx for the feedback. I set it on the car and it does just that now. Everything good. Learning processes......
Wires are all round and so is the raceway.What do you mean by the shape and the third fits in differently than the second? Are there conductors that aren’t round? And fill % is about cross section so the shape doesn’t matter. Whether a stranded wire is round or flattened oval, it’ll still have the same cross section a fill %. 2x 6ga thhn are going to fit the same way in 1/2 emt whether another conductor is there or not. Having a third conductor will help with pulling through bends but it doesn’t change the shape and fit of the 2x 6ga conductors.