To follow up on the conversation our house is finally at the electrical stage and the electrician ran some calculations and thinks it is too much load to have two 60amp, therefore they were recommending only one.
I’m just really at a loss of what to do. I have one HPWC I received as a referral gift. I also anticipate another Tesla in the future. Should I keep the 60amp line and have it go to the one HPWC for now and then when we get another Tesla either daisy chain or break it into two 30amp circuits at a later date? Should I up the one to higher than 60amp then? Is there a NEMA receptacle for higher than 60amp? Appreciate the recs!!
I don't see any reason to go higher than 60A unless you're planning on a Cybertruck (maybe - and even then it probably doesn't matter THAT much). 48A is the maximum for Model 3 (Cybertruck will nearly certainly be higher). Like I said, even for Cybertruck 11.5kW is probably going to be fine nearly all the time (with a Cybertruck ~180kWh battery it'll be a 14-hour charge to 100%). So no reason to go higher than 60A, unless you have a legacy vehicle with 20kW charger option.
I would ask the electrician what is the maximum load that the load calculations support, and just install one 60A and then allocate the remaining balance to the other one. Or if that ends up being just 10A or something, just reduce the 60A to 40A or something, or whatever distribution you feel is best. (I would tend to try to max out one of them just so you have that option.)
240V/20A is perfectly fine in nearly all situations. And if you have a 60A charger as well, it really won't matter. I'm sure that one vehicle will be the one that "typically" needs the most charging. And if you really have to you, you can always switch spots on the rare occasion where the one that needs the fast charge isn't in the right spot.
Better option if you're just doing hard-wired WCs: Two Wall Connectors can also do communication, so you can also do a maximum rate circuit, max that load calcs support, and just let them arbitrate on the same circuit. I can't remember why that wasn't the original solution here (haven't gone back to read the thread).
Obviously that doesn't work if for some reason you want a J-1772 or want that option in the future (unless in the future J-1772 EVSEs also can communicate - which it seems like they will at some point but undoubtedly there will be no uniform comm standard, so it will just be all stupid and you won't be able to mix and match).
EDIT: reading back on this thread, it looks like Tesla is also being all stupid about this with V3. Anyway, obviously load-sharing is the best option, but if you can't do that, just allocate sensibly and max out the load capability according to the load calc from the electrician. Have him figure out the maximum allowed.