Per the spec sheet, it's a 50A breaker.
My guess, as we are all guessing here, is that Tesla expects the plurality of its installs going forward will be only one PW. Since they are requiring PWs on every install, all those solar only installs are going to become solar + 1 PW installs. So PW+ is optimized for that case.
As to how you could extend the PW+ design to handle multiple PWs, the easiest solution is to get it listed as a Power Control System, 2020 NEC 705.13. Then in jurisdictions that follow the 2020 NEC or will allow early use of it, the PW+ connection to the main panel can be increased in size without the need to qualify under the 120% rule or its ilk. The system controller in the PW+ will monitor the grid draw and ensure that grid current + inverter current < main panel busbar rating at all times.
Cheers, Wayne