Question on HPWC install, breakers and settings. About to install my HPWC in my 100A Subpanel in the garage, which currently houses my NEMA 14-50 on a 50A breaker. Since the subpanel comes off my main panel, which is a 200A service split into two separate 100A main breakers, I don't want to set the HPWC for a full 80A draw, as that would only leave 20A for the rest of the house (or half of it, anyway). Someday I will upgrade that main panel to a single 200A breaker, which will allow me to set the HPWC for potential maximum 80A draw. Because of the fuse issue and this limitation, I want to limit my draw to 60A.
So my question is this: can I install a 100A breaker in my subpanel and wire this to the HPWC, and then set the dip switches to 60A? I could then set the draw rate in the car to less than 60A, saving the 60A for when I need a faster charge, and ensuring I don't trip the split 100A main for the remaining 40A in half of the house. Or should I be matching the breaker to the dip switch setting, and only install a 60A breaker?
FlasherZ, I saw earlier that you said limiting the HPWC to 60A via the dip switches would be fine. Was that assuming the HPWC was wired to a 100A-breaker?
I don't want to introduce any safety issues here. I am fine living with a reduced breaker size for the HPWC, I could even live with a 50A for that matter. But I do have twin chargers and would love to be able to dial it up if the situation arises where I need a fast charge. What size breaker should I put this on in my subpanel? My electrician seemed to indicate that the 100A would be fine, especially if we could limit the HPWC or car as needed.