eprosenx
Active Member
Update: I had an electrician do an on-site inspection. He says the wire in the conduit between the main breaker and the subpanel in my garage is #4 THHN copper. He says it's good for 100A, so the only necessary hardware change is to replace the 70A main breaker with 100A. I submitted the request to my HOA. If they say yes, I should be good to go. Crossing fingers.
Awesome! That jives with my understanding of code when you factor in the 83% rule which you are allowed to do on 100a service feeds.
So have you determined that your panel is not one of the hazardous ones and so just adding a new quad tandem breaker will be safe?
What size circuit will you add then for your car? Are you going to do just a receptacle for the UMC or are you going to do a Wall Connector? Since you will be getting another 30 amps of capacity you could go larger than a 30a circuit potentially. Perhaps a 14-50 which would need 32a of continuous capacity (40a) if you are using a UMC Gen 2. I would still wire it with wire for a 50a circuit regardless (6awg instead of 8awg).