Then where does the other 100Amp go to and how do you turn it off?The 100 amp breaker in that panel feeds a sub panel in the garage.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Then where does the other 100Amp go to and how do you turn it off?The 100 amp breaker in that panel feeds a sub panel in the garage.
Then where does the other 100Amp go to and how do you turn it off?
Then where does the other 100Amp go to and how do you turn it off?
This is why I questioned whether he even had 200 amp service to begin with. There is no other panel and the ‘other 100 amps’ is just not used.
All the electricians seem to have fled this thread, and I am not one, so this is just my guess. This main panel (as shown in the pictures) does not have a single main breaker disconnect. Instead it has multiple breakers that must all be flipped off to turn off all power to the house. So in the original,picture, you’d have to flip off the 100A, 50A and 15 A breakers to turn off all the power. The panel can still be rated for 200A and likewise the meter and feed.
There is another panel inside the garage which is what that 100A breaker feeds. The 50 and 15 on the bottom are for the AC and AC signaling. So by shutting off the 100A shown you're shutting off everything in the house.This is why I questioned whether he even had 200 amp service to begin with. There is no other panel and the ‘other 100 amps’ is just not used.
There is another panel inside the garage which is what that 100A breaker feeds. The 50 and 15 on the bottom are for the AC and AC signaling. So by shutting off the 100A shown you're shutting off everything in the house.
It is a meter main panel with multiple feeds. Not uncommon especially with larger services. Most 400 amp panels are setup that way where there are 2) 200 amp breakers and the ability to have 1 or 2 additional breakers. Some times there is a breaker panel as part but sometimes it just feeds other sub-panels.
The additional breaker spaces are typically used for large loads such as the HVAC or for solar installs. Since it isn't uncommon for the large load to be near the panel and that allows the sub-panel and wire to be sized smaller.
So it is likely the meter socket and bus bars are rated for 200 amp. They only needed a 100 amp sub-panel so they put a 100 amp breaker to feed it.
Nice fixes. For future reference in case anyone wonders about this, hardwired EVSEs like the HPWC don’t need a GFCI breaker since they have a built in GFCI. No harm in adding an extra one though.
Actually there is harm in installing an EVSE on a GFCI breaker. Two posts above have already said it so at the risk of repeating... A lot of cars require the full 20 ma of unbalanced current in order to start charging. Sometimes a Model S or X will require more than 5 ma which is what the breaker's trip point is. It might seem like everything is fine until one day you'll wake up and find out your car didn't charge. Tesla's installation instructions specifically state NOT to use a GFCI breaker.Nice fixes. For future reference in case anyone wonders about this, hardwired EVSEs like the HPWC don’t need a GFCI breaker since they have a built in GFCI. No harm in adding an extra one though.
Don't know about the OP's area, but in San Diego you can't have any of that stuff within 36" of the gas meter or it won't pass inspection, assuming you're going to have it inspected.