WOW someone is having a bad day. I'm lying that I am pulling 64 amps at 240V? I guess the electronics in the Tesla are bad as I clearly see 242V at 64 amps in the VDS shot below. This is less of a voltage drop I see with 30 amp public charging and NEMA 14-50's at campgrounds.
View attachment 72001
You had me worried so I rechecked the plug and wire run with my IR meter and while there is a temperature rise after 20 minutes; 4 degrees F is well within tolerances and well below a Model S cable.
I see you are the next state over from me so if you need a charge just off of I26 you might want to find an option B unless you want to check for yourself.
*sigh*
First, this doesn't really prove anything. While, this image just shows you charging at 64A@242V... doesn't mean this is with your illegal outlet setup, doesn't show the starting voltage, etc. The voltage drop is going to be at least several percent. I can't speak to the Roadster's voltage reading accuracy, but I know what the Model S shows on the dash is +/- 1V of what I read directly at the rear of the charge port inside the trunk. (Edit: To clarify, if you look at my earlier post, I wasn't saying that you charging at 64A was the lie, it was the ridiculous lack of temperature rise you report at that rate)
I'd also guess your IR meter isn't really all that accurate (or is being used improperly) if you're only seeing a 4F rise at any point on the wiring or outlet using the setup you described. Even pulling 40A @ 240V on #6 wire, the legal setup, will cause a nominal temperature rise. If you're basing your entire safety argument on a cheap IR meter's readout... I'd highly suggest opening your eyes a bit wider, ie through a FLIR or similar IR cam.
4F rise is just ridiculous and wrong unless you have an A/C unit cooling the plug and wiring or something equally strange.
So that people have something to compare, and to prove that this 4F rise at 64A is ridiculous, here are some normal temperature rise pics from Mr. FLIR that I've taken at various times during my solar project install:
FLIR image of #6 wire under load at 32A/240V (half of what you're pulling and well below the rated amount) showing a ~25F temperature rise above ambient after 45 minutes.
Another pic of #6 wire, this time NM cable (6/2 Romex) under 30A/240V load for ~10 minutes. More than 5F rise above ambient already at this load, less than half of yours.
FLIR image of my right side 200A electrical panel showing two sets of #2 wire running to my two HPWCs, both running at 80A (only 16A more than you're pulling on #6 wire which is roughly 1/3rd the amount of copper), showing a 50F (~27C) temperature rise on the conductors after 90 minutes. (Breaker runs a bit hotter than the conductors, but this is normal)
Just to drive home that the whole 4F rise on #6 @ 64A is impossible, here is
#3/0 wire under 240V/85A load (HPWC at 80A + a few 120V loads). The #3/0 wire is literally ~7x more copper, and it still has a temperature rise of about 5-6F after ~40 minutes.
A picture is worth 1000 words... and a FLIR pic is worth 64,000 data points. (Edit: I'll point out that the temperatures readings from FLIR of the conductors above are within 1% of what the math says they should be for the given load and wire size... the same math that says at least a 45C/88F rise in the #6@64A)
If you're pulling 64A through #6 wire AND a NEMA 14-50 plug and outlet AND 30' of cable, then you said you only saw even the 25F rise like I'm showing in the first FLIR pic at 32A... I'd still have to say you were lying. Perhaps "lying" is a bit harsh. Perhaps "misinformed" may fit better? You're definitely not reporting a real temperature read, that's for damn sure.
I'll just suggest you rent/borrow/buy a decent FLIR cam, look directly at the wiring/outlet/breaker/etc while under your 64A load. If you rent one, do an actual test with enough pics (or better a video) that can at least somewhat prove it's not fake, and I'm wrong and you actually only get a 4F increase in temp anywhere on your wiring/outlet/etc... then you'll need to call a chemist to figure out what your wiring is made out of because it certainly isn't #6 copper wire.
I'm certainly not going to drive 120-ish miles just to end up telling you what I've already told you here... your setup is illegal and your setup is a fire and safety hazard. The 2008 NEC is law in Tennessee. Period. Sorry if I'm a bit harsh on stuff like this, but, I wouldn't want anyone doing this. For example, if I found out my neighbor was doing what you're doing and putting my home and property at risk... call me crazy, but I'd probably call the police.
Since you're obviously not going to change your setup to be legal no matter what anyone says this discussion between you and I is over and I'm done wasting my time with it.
- - - Updated - - -
*Note quickly did math, so could be complete wrong with errors.
#6 wire size over
30 feet is 0.012 ohms.
244v starting voltage x 0.012 ohms = voltage drop of 2.928v
244v starting voltage - 2.928v voltage drop = 241.072, guessing the roadster is rounding up i.e. displaying 242v.
2.928v drop x 64 amps = 187.392 watts over 30 feet run.
You're forgetting losses in the plug/outlet, plus the cable on the HPC, plus the charge connector.
Admittedly, I did my math with a 240V starting voltage which gave me a lower final voltage, but the temperature calcs still remain unchanged +4V since the amperage is the same.
In any case, only a 4F rise on the copper conductor is just impossible, which is the part I said was a lie, not the voltage drop.
Edit: For s**ts and giggles and ran the numbers as if the #6 conductor were made of silver instead of copper (less resistance)... and I still come up with more than 4F rise after 20 minutes. lol.