Just had my Nema 14-50 outlet hooked up yesterday, with a 50 amp breaker. I buried about 60 feet of what I thought was 6/3, but when the electrician got here he pointed out they had given me 8/3 wire. He thought is would be OK since the UMC says 32 amps is what it operates at, and hooked it all up--works fine. Should I be OK?? sure don't want to dig all that back up!!! I "assumed" they gave they gave me the right wire--- thoughts??? thanks....
 
To meet code you would need to swap the breaker for a 40 amp breaker, unless the wire isn't NM-B/UF-B and is actually THWN/etc. With a 50 amp breaker the wire isn't capable of handling all 50 amps, regardless of the 'intended load' not being able to pull above 32A.

Did you actually pay for 6/3 wire? If so, I'd raise hell, cause 8/3 wire should be a good bit cheaper than 6/3 and 60ft of it isn't cheap.
 
First, what kind of 8/3 did you get? If it's buried outside it needs to be the outdoor-rated, type UF-B. This is NOT the same as standard indoor Romex (type NM-B), which will not last long outside and isn't necessarily waterproof.

Second, 8 gauge wire is fine but you need to change the breaker to a 40 amp one. Type UF-B or NM-B 8 gauge is only rated to a max 40A. Your electrician should not have put a 50A breaker on it.

Whether you use 8 or 6 gauge, your mobile connector will only pull 32A. So either way you're getting the max charging rate you can in a model 3. But you need to make sure the correct breaker is on the circuit. It is perfectly fine to put an 14-50 outlet on a 40 A breaker, since there's no such thing as a 14-40 outlet.
 
First, what kind of 8/3 did you get? If it's buried outside it needs to be the outdoor-rated, type UF-B. This is NOT the same as standard indoor Romex (type NM-B), which will not last long outside and isn't necessarily waterproof.

Second, 8 gauge wire is fine but you need to change the breaker to a 40 amp one. Type UF-B or NM-B 8 gauge is only rated to a max 40A. Your electrician should not have put a 50A breaker on it.

Whether you use 8 or 6 gauge, your mobile connector will only pull 32A. So either way you're getting the max charging rate you can in a model 3. But you need to make sure the correct breaker is on the circuit. It is perfectly fine to put an 14-50 outlet on a 40 A breaker, since there's no such thing as a 14-40 outlet.

Good note on the UF-B vs. NM-B. I'd assume an electrician should know not to bury NM-B... but who knows. OP, if the wire you bought is actually NM-B (which tends to be the cheapest wire available), you do need to pull that wire and rebury with actual UF-B (or another underground burial rated wire). NM-B isn't allowed to be used outside (buried, in conduit, or otherwise) period.
 
  • Informative
Reactions: davewill
To meet code you would need to swap the breaker for a 40 amp breaker, unless the wire isn't NM-B/UF-B and is actually THWN/etc. With a 50 amp breaker the wire isn't capable of handling all 50 amps, regardless of the 'intended load' not being able to pull above 32A.

Did you actually pay for 6/3 wire? If so, I'd raise hell, cause 8/3 wire should be a good bit cheaper than 6/3 and 60ft of it isn't cheap.
I did pay for 6/3--goig to deal with that...thanks
 
First, what kind of 8/3 did you get? If it's buried outside it needs to be the outdoor-rated, type UF-B. This is NOT the same as standard indoor Romex (type NM-B), which will not last long outside and isn't necessarily waterproof.

Second, 8 gauge wire is fine but you need to change the breaker to a 40 amp one. Type UF-B or NM-B 8 gauge is only rated to a max 40A. Your electrician should not have put a 50A breaker on it.

Whether you use 8 or 6 gauge, your mobile connector will only pull 32A. So either way you're getting the max charging rate you can in a model 3. But you need to make sure the correct breaker is on the circuit. It is perfectly fine to put an 14-50 outlet on a 40 A breaker, since there's no such thing as a 14-40 outlet.
It is the correct UF-B wire , just not the 6/3 I asked for. I think i will have the breaker changed to 40 amp--many thanks!!
 
Thanks to all of you for all the help, after I raise hell at the supply company, I am going to get a 40 amp breaker, and ask the electrician to switch out the 50 amp for a 40 amp. It is the right type wire UF-B--buried in conduit--just a lighter gauge than I thought I was getting.
 
A 40A breaker and 32A charging on a Model 3 gives about 29 miles of range per hour. That's plenty good enough for most people. I wouldn't sweat it. If they give you the cost difference back, I wouldn't lose sleep over it at this point.
Yeah, no perspiration..........however...........if that electrician is a friend and he installed a 50A breaker on 8/3, he shouldn't be a friend. If he's licensed, or works for a licensed electrician, I would make it a point NEVER to use that company EVER again for electrical work.
 
Yeah, no perspiration..........however...........if that electrician is a friend and he installed a 50A breaker on 8/3, he shouldn't be a friend. If he's licensed, or works for a licensed electrician, I would make it a point NEVER to use that company EVER again for electrical work.
Right--understood about the electrician--after he slept on it he too recommends changing to a 40 amp breaker, which is what I will have him do. The charging speed is plenty good enough for me. thanks to you all!!