Hi everyone. Normally, we plan for 80% utilization for a given circuit. If you have a 40A circuit, you can charge at 32A for example. 50A can charge at 40A, and 60A can charge at 48A. You get the idea.
I have a dedicated 60A circuit running 5 feet with #6 wire. It can easily handle the max charge rate of my model Y at 48A. This issues is that I have a 50A 14-50 plug in line.
Now, I know to pass code, I can swap the 60A breaker for a 50A and the problem is solved. This is what I would do if I was selling the house or had any concern of anyone plugging in a load greater than 50A. Since I'm the only one using it and I know they only load will ever be my car and it tops out at 48A and the plug is rated at 50A, do you think its OK to leave it there?
I have a Tesla Wall connector and it is currently set to charge at 40A and I'm wondering about cranking it up to 48A. Thoughts?
Hi everyone. Normally, we plan for 80% utilization for a given circuit. If you have a 40A circuit, you can charge at 32A for example. 50A can charge at 40A, and 60A can charge at 48A. You get the idea.
I have a dedicated 60A circuit running 5 feet with #6 wire. It can easily handle the max charge rate of my model Y at 48A. This issues is that I have a 50A 14-50 plug in line.
Now, I know to pass code, I can swap the 60A breaker for a 50A and the problem is solved. This is what I would do if I was selling the house or had any concern of anyone plugging in a load greater than 50A. Since I'm the only one using it and I know they only load will ever be my car and it tops out at 48A and the plug is rated at 50A, do you think its OK to leave it there?
I have a Tesla Wall connector and it is currently set to charge at 40A and I'm wondering about cranking it up to 48A. Thoughts?