indeed as the demand went down it looks like the wind was following, though that could be coincidence).
I think that was mostly still controlled by ccgt, although not exclusively, ie hydro.
I was looking at this last night in response to this question and wanted to put to clear graphs together, but I couldn't do clear so left it till later when I could be sure I was looking at like for like time periods. I was using the raw Elexon data from
bmreports
However, what it did show, up to around 21:00, was that if you looked at the individual sources of energy, many were quite flat. However ccgt ( combined cycle gas turbine) was not and visually there appeared to be a fairly good correlation to demand. I say visually, at I wanted to put a more numerical set of data together before replying.
However, very briefly, to prevent this question going stale, I'll omit the numerical data and keep with the visual hence this post.
Electricity Data Summary | BMRS is a good one, system demand (left) and generation by fuel type (right).
This is this mornings data. 21:00 last night, whilst different, and huge quantity of wind, the outcome remained the same.
Visually the evidence is as follows. Note x axis scale differs between graphs, so demand is more compressed in x axis than generation - part of the reason why I was holding off a quick reply.
Removing the minor 'flat' fuel types and less flat interconnects (they make little difference to the shape of the graph and removal adds clarity). Removing ccgt, the typical marginal source, the first pair of graphs show a largely flat total curve, certainly not following the system demand.
However, adding back in ccgt, you see that the generation curve now tracks the system demand quite closely. A first glance conclusion is that ccgt remains the marginal source as it is the source that has significant control over the generation matching demand.
So based on this, even when wind is major proportion of generation, it is ccgt that is the primary energy source that is used to balance generation with demand, ie when someone flicks that switch. But other sources were also at work (they are better for fine tuning but not the primary method) like hydro (typically pumped storage), and some of the interconnects (which we have no control over their source of energy) - see below.
What is good though, is that average generation this weekend was significantly biased to renewable. But these events are currently, not a regular occurance. So the round trip losses are coming from more fossil fuelled sources.
As for solar time shifting, if this is the primary requirement for battery, the a Powerwall v2 being AC coupled is not the best choice. A DC coupled storage system is a better choice as solar goes direct into the battery with no AC/DC/AC losses, so that solar stored energy is as efficient as had it been used direct from solar conversion wise - both would typically use the same DC/AC inverter so the only losses incurred are in storage itself. Ironically, Powerwall v1 worked this way as it was a DC coupled system, but in a FiT based system, it had the disadvantage a very blurred line between battery storage and solar generation and the total generation meter - the meter measuring what you got paid on, which would have worked against FiT payments. So anyone wanting a battery storage system primarily for time shifting their solar, should also be considering a DC coupled system, ie not a Powerwall v2.